Based on the IFC the determining factor for the standpipe is the lowest
level of fire dept. access. Not the location of the FDC.

905.3.1 Building height. Class III standpipe systems shall
be installed throughout buildings where the floor level of the
highest story is located more than 30 feet (9144 mm) above
the lowest level of the fire department vehicle access, or
where the floor level of the lowest story is located more than
30 feet (9144 mm) below the highest level of fire department
vehicle access.
Exceptions:
1. Class I standpipes are allowed in buildings
equipped throughout with an automatic sprinkler
system in accordance with Section 903.3.1.1 or
903.3.1.2.

5. In determining the lowest level of fire department
vehicle access, it shall not be required to consider:
5.1. Recessed loading docks for four vehicles
or less, and
5.2. Conditions where topography makes
access from the fire department vehicle to
the building impractical or impossible.


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Knight
Sent: Thursday, June 25, 2009 9:44 AM
To: [email protected]
Subject: Standpipe FDC Access

I have a situation where there is a four story building that is 33' to the
lowest level of fire department vehicle access on the west side.  The east
side of the building is only 23' above the lowest level of fire department
vehicle access.  My question is if the FDC is located on the east side of
the building can the standpipe requirement be eliminated since the 23' is
less than the 30' required by IBC 905.3.1?

Thanks,

Bob Knight, CET
1660 Hill Rd
Melba, Idaho 83641
(208) 318-3057
(208) 495-2057 fax
[email protected]
www.firebyknight.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to