The location of the FDC has absolutely nothing to do with the question of standpipes or not. It's all about FD access. The presence of an FDC would strongly suggest access to that point but not always. The absence of the FDC from a particular area suggests nothing about access.
Only the AHJ can tell you how they interpret access. There is one rule of thumb if you can drive a fire truck there it's access. So a parking lot for cars is access under that rule. The other rule of thumb is required access. The code only requires you be able to park a fire truck within 150 of all points of the perimeter. So from the road maybe the parking lot is not part of the REQUIRED access. IMHO and based on experience if there is a parking lot at 33' you will end up with standpipes 99% of the time. Tell them to find 3' of dirt or sink the foundation 3' or some combination of the two. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bob Knight Sent: Thursday, June 25, 2009 11:39 AM To: [email protected] Subject: RE: Standpipe FDC Access This next part is completely hypothetical on my part because I don't have all the information in front of me. What if the lower potion of the building doesn't have fire department access? Say that it's a parking area for the residents and there is no FD access. Then the FDC is routed to the east side which has the highest level of floor occupancy 23' above the FD access. Would a standpipe be required in this situation? Thanks, BK -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, June 25, 2009 10:30 AM To: AFSA Forum Subject: Re: Standpipe FDC Access Not at all. I'm agreeing that a standpipe is required by the letter of the code, and that the FDC should be on whatever side or access lane the FD wants it to be, regardless of height. Sent from my Verizon Wireless BlackBerry -----Original Message----- From: "Bob Knight" <[email protected]> Date: Thu, 25 Jun 2009 09:04:51 To: <[email protected]> Subject: RE: Standpipe FDC Access Steve, >From one addict to another, are you saying that if the FD is ok with the FDC on the east side of the building (23' access height), then the standpipe is not required? Thanks, BK -----Original Message----- From: [email protected] [mailto:[email protected] <mailto:[email protected]> ] On Behalf Of Steve Leyton Sent: Thursday, June 25, 2009 9:49 AM To: [email protected] Subject: RE: Standpipe FDC Access Wherever the Fire Official requests that it be located. Steve L. On vacation but still checking e-mail because I'm an addicted loser and I admit it. ________________________________ From: [email protected] on behalf of Bob Knight Sent: Thu 6/25/2009 8:44 AM To: [email protected] Subject: Standpipe FDC Access I have a situation where there is a four story building that is 33' to the lowest level of fire department vehicle access on the west side. The east side of the building is only 23' above the lowest level of fire department vehicle access. My question is if the FDC is located on the east side of the building can the standpipe requirement be eliminated since the 23' is less than the 30' required by IBC 905.3.1? Thanks, Bob Knight, CET 1660 Hill Rd Melba, Idaho 83641 (208) 318-3057 (208) 495-2057 fax [email protected] www.firebyknight.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum <http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4188 (20090625)__________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com <http://www.eset.com> <http://www.eset.com/ <http://www.eset.com/> > _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum <http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4188 (20090625)__________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com <http://www.eset.com> _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)