Parking usually does not impede FD access but I'll let the AHJ's  
address that.  As Thom addressed earlier, if you physically can not  
reach a portion of the exterior (say one side of the building is on  
the water or the side of a cliff) then only the other three sides are  
looked at.

Roland

On Jun 25, 2009, at 9:38 AM, Bob Knight wrote:

> This next part is completely hypothetical on my part because I don't  
> have
> all the information in front of me.  What if the lower potion of the
> building doesn't have fire department access?  Say that it's a  
> parking area
> for the residents and there is no FD access.  Then the FDC is routed  
> to the
> east side which has the highest level of floor occupancy 23' above  
> the FD
> access.  Would a standpipe be required in this situation?
>
> Thanks,
> BK
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Thursday, June 25, 2009 10:30 AM
> To: AFSA Forum
> Subject: Re: Standpipe FDC Access
>
> Not at all.  I'm agreeing that a standpipe is required by the letter  
> of the
> code, and that the FDC should be on whatever side or access lane the  
> FD
> wants it to be, regardless of height.
>
>
> Sent from my Verizon Wireless BlackBerry
>
> -----Original Message-----
> From: "Bob Knight" <[email protected]>
>
> Date: Thu, 25 Jun 2009 09:04:51
> To: <[email protected]>
> Subject: RE: Standpipe FDC Access
>
>
> Steve,
>> From one addict to another, are you saying that if the FD is ok  
>> with the
> FDC
> on the east side of the building (23' access height), then the  
> standpipe is
> not required?
> Thanks,
> BK
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]
> <mailto:[email protected]> ] On Behalf Of Steve
> Leyton
> Sent: Thursday, June 25, 2009 9:49 AM
> To: [email protected]
> Subject: RE: Standpipe FDC Access
> Wherever the Fire Official requests that it be located.
>
> Steve L.
> On vacation but still checking e-mail because I'm an addicted loser  
> and I
> admit it.
> ________________________________
> From: [email protected] on behalf of Bob Knight
> Sent: Thu 6/25/2009 8:44 AM
> To: [email protected]
> Subject: Standpipe FDC Access
>
>
> I have a situation where there is a four story building that is 33'  
> to the
> lowest level of fire department vehicle access on the west side.   
> The east
> side of the building is only 23' above the lowest level of fire  
> department
> vehicle access.  My question is if the FDC is located on the east  
> side of
> the building can the standpipe requirement be eliminated since the  
> 23' is
> less than the 30' required by IBC 905.3.1?
> Thanks,
> Bob Knight, CET
> 1660 Hill Rd
> Melba, Idaho 83641
> (208) 318-3057
> (208) 495-2057 fax
> [email protected]
> www.firebyknight.com
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> <http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum>
> For Technical Assistance, send an email to: [email protected]
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> __________ Information from ESET NOD32 Antivirus, version of virus  
> signature
>
> database 4188 (20090625)__________
> The message was checked by ESET NOD32 Antivirus.
> http://www.eset.com <http://www.eset.com>  <http://www.eset.com/
> <http://www.eset.com/> >
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> <http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum>
> For Technical Assistance, send an email to: [email protected]
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> __________ Information from ESET NOD32 Antivirus, version of virus  
> signature
> database 4188 (20090625)__________
> The message was checked by ESET NOD32 Antivirus.
> http://www.eset.com <http://www.eset.com>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to