And it sounds like a homemade one.

On Sat, Jun 27, 2009 at 9:00 AM, <[email protected]> wrote:
> You are probably looking at an excess pressure pump used to keep system 
> pressure high to avoid false alarms due to pressure surges.
> Mike Wisneski
> Sent from my BlackBerry® smartphone with Nextel Direct Connect
>
> -----Original Message-----
> From: [email protected]
>
> Date: Sat, 27 Jun 2009 11:38:16
> To: <[email protected]>
> Subject: mercoid switch on wet riser
>
>
> I saw something which I do not understand and hope someone can explain
> this to me.
> A 35 year old wet system, manifold with 2 alarm valves. There is a
> electric flow switch on each riser, I think added recently.
> The valves were trimmed with the normal motor gongs, etc.
> The system side gauges are piped together between the two risers, with
> check valves, a mercoid switch labeled pump switch, and another mecoid
> switch labeled alarm switch.  On this piping there are 3 check valves
> and a small test cock, presumably for testing.
> There is a small pump with 1/2 in inlet from supply side of valve 2,
> which discharges into the pressure gauge piping described above.
>
> What is the purpose of this? Was it standard at one time?
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to