Hello George,

That was what the ADT (FTW/DLS) office I was in put in for the waterflow switch 
also.

Monday, June 29, 2009, 7:54:47 AM, you wrote:

> If you had a jockey pump and I'll assume a fire pump, why would you need an
> excess pressure pump?
> glc

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Coastal
> Sent: Monday, June 29, 2009 6:49 AM
> To: [email protected]
> Subject: Re[2]: mercoid switch on wet riser

> Hello bverhei,

> So I am not the only one that remembers the old ADT 6121. When I started
> with them back in 1978 they were on 99% of the Wet risers. Had to be careful
> with the setup on em as it was easy to exceed the rating of fittings when
> you were downstream of a Jockey pump.

> Sunday, June 28, 2009, 8:09:43 PM, you wrote:

>> Excess pressure pump. The definitive solution where someone in the range
> of AHJ's takes
>> stopping false alarms due to pressure surges. I do mean stopping, not
> reducing. Required
>> in Vancouver (and the rest of B.C.?). Seems New Zealand is on the list. 

>> Can be done without the Gamewell (ADT?) unit. Not required to be listed
> for fire
>> protection service, unless unit also act as the switch for the fire alarm
> system interface.

>> Yours, 

>> Bruce Verhei 

>> ----- Original Message ----- 
>> From: "Tom Duross" <[email protected]> 
>> To: [email protected] 
>> Sent: Sunday, June 28, 2009 7:51:04 AM GMT -08:00 US/Canada Pacific 
>> Subject: RE: mercoid switch on wet riser 

>> What Todd said. They probably replaced the original compound type with a 
>> mercury one. 
>>>From what I know, Gamewell isn't making them anymore. I think they ceased 
>> last summer, I drove out to get a diff. switch and they told me. 
>> Just as an aside, my grandfather is on the patent for this and a few other

>> things Gamewell made before and after the depression when they were in 
>> Newton, MA. I have a beautiful one I "kept" in my basement along with a 
>> couple of those McCullough type switches I posted about last summer too in

>> really nice shape. 
>> Of course, nothing official but my Dad has a picture of him and the crew 
>> taken in the shop after another patent was awarded. Funny coincidence. :) 

>> TD 
>> Go Red Sox! 

>> The old Gamewell excess pressure pumps had a very homemade look about
> them. 
>> And that sounds like what is being described. Used to be required in
> Canada 
>> and parts of Europe don't know if they still are.. 

>> Richard 


>> Sounds like an excess pressure pump. These were used in areas with a 
>> lot of pressure fluctuations to prevent false alarms. This was before 
>> flow switches with delays. Gamewell was famous for these but 
>> Firematic made a fairly simple version of the same thing. Some towns 
>> (at least in this part of the world) required them 



>> At 11:38 AM 6/27/2009, you wrote: 
>>>I saw something which I do not understand and hope someone can explain 
>>>this to me. 
>>>A 35 year old wet system, manifold with 2 alarm valves. There is a 
>>>electric flow switch on each riser, I think added recently. 
>>>The valves were trimmed with the normal motor gongs, etc. 
>>>The system side gauges are piped together between the two risers, with 
>>>check valves, a mercoid switch labeled pump switch, and another mecoid 
>>>switch labeled alarm switch. On this piping there are 3 check valves 
>>>and a small test cock, presumably for testing. 
>>>There is a small pump with 1/2 in inlet from supply side of valve 2, 
>>>which discharges into the pressure gauge piping described above. 
>>> 
>>>What is the purpose of this? Was it standard at one time? 
>>> 

>> _______________________________________________ 
>> Sprinklerforum mailing list 
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
>> For Technical Assistance, send an email to: [email protected] 

>> To Unsubscribe, send an email to:[email protected] 
>> (Put the word unsubscribe in the subject field) 
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]

>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)






-- 
Best regards,
 Charles Thurston                            mailto:[email protected]
  Coastal Fire Protection