Sounds like an excess pressure pump. These were used in areas with a 
lot of pressure fluctuations to prevent false alarms. This was before 
flow switches with delays. Gamewell was famous for these but 
Firematic made a fairly simple version of the same thing. Some towns 
(at least in this part of the world) required them



At 11:38 AM 6/27/2009, you wrote:
>I saw something which I do not understand and hope someone can explain
>this to me.
>A 35 year old wet system, manifold with 2 alarm valves. There is a
>electric flow switch on each riser, I think added recently.
>The valves were trimmed with the normal motor gongs, etc.
>The system side gauges are piped together between the two risers, with
>check valves, a mercoid switch labeled pump switch, and another mecoid
>switch labeled alarm switch.  On this piping there are 3 check valves
>and a small test cock, presumably for testing.
>There is a small pump with 1/2 in inlet from supply side of valve 2,
>which discharges into the pressure gauge piping described above.
>
>What is the purpose of this? Was it standard at one time?
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to