Sounds like you're in pretty good shape from an information standpoint.

So if you've already gotten the foam mfgr. to help determine densities, (not 
straight NFPA 30 densities hopefully) then how about just giving him a call and 
ask about the P.G.?
 
I'm sure the PG system is cheaper as long as it's maintained and setup 
properly.  That's where the gamble lies.  

Now the point to consider is that once a sprinkler fuses, the PG will be 
released at that point followed by water, but what is not known is how PG from 
the system will migrate to the discharge point and eventually mix with the 
discharging foam.

Since there's no foam in the system until you have a discharge, you may dilute 
what is present in the system enough to where it's not an issue at all.

But remember, there have been discussions here about glycol based systems 
discharging onto heaters and other instances where the glycol has become a fuel 
to the fire upon initial discharge.  

All my design guides point to preaction for areas subject to freezing and for 
wet systems say initial fill to be water.  Couldn't find any support anywhere 
for Glycol in foam systems.
 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Monday, July 06, 2009 12:12 PM
To: '[email protected]'
Subject: RE: NFPA 30 - and Propylene Glycol

We've got all the MSDS; all of the liquids classifications and we know the 
densities required.  This issue is limited to the use of Prop glycol antifreeze 
on a 'wet' AFFF sprinkler system for flammable liquids storage.  (FYI - The 
liquids range in classification from IB to IIIB, many miscibles, and both poly 
and metal drums - all 55 gal. drums on end, up to two high).

PG doesn't seem wise unless someone (manufacturer) can prove to me it is 
compatible with the AFFF in the pipes; AND that there isn't an adverse affect 
from dumping PG on the flammable liquids fire prior to the foam. It's use over 
preaction is based on cost, according to the contractor. Don't yet know if they 
have the means included to fully drain the PG every year for testing and refill.

Mark
-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, July 06, 2009 7:40 AM
To: [email protected]
Subject: RE: NFPA 30 - and Propylene Glycol

Uh, no.  If there is a problem with freezing they can use a single interlock 
preaction foam-water system.  You don't mix P.G. in it, that won't work.

The preaction conforms to NFPA 30, dry systems are not permitted.

Now before anyone starts anything, there needs to be an analysis of the 
chemicals being stored to determine the appropriate design criteria for 
protection of the area.  Just because he's storing flammables doesn't mean you 
automatically go to AFFF, you may need AR-AFFF or some other means of 
suppression may be acceptable.  I've found that most people don't know the 
difference between flammable and combustibles and there is a difference when 
determining protection schemes.  Plus the density depends on the chemicals 
being stored.  There's no magic number you can just plug in.

Get ALL the MSDS info on everything in the storage area.  Don't just ask for or 
get the "flammables".  Get everything.  There are code issues at hand 
concerning how much of certain chemicals can be stored inside

Once you've determined what the chemicals are, their classifications, 
quantities, etc. then you can check codes to determine whether he can actually 
store them inside or not, if anything needs to be done to the building or if 
they can store without any changes.  Then contact your favorite foam vendor and 
have their chemist look at the chemicals you're dealing with and give you a 
recommendation on protection.

MSDS info is invaluable but don't rely on just one mfgr.  Get a copy of the 
chemicals from a couple of different suppliers since information on MSDS can 
vary in it's completeness.  These things will also give you recommendations for 
fire fighting measures and warn if something is reactive or if something 
special is needed.

Someone has a lot of homework to do.


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Thursday, July 02, 2009 4:11 PM
To: '[email protected]'
Subject: NFPA 30 - and Propylene Glycol

Forum:

I have a client who wants to store flammable liquids in a cold-storage 
warehouse.  They would like to use an AFFF sprinkler system with propylene 
glycol to prevent freezing.

I am not a fan of this idea and won't support it for a number of reasons.

Do any of you have any views you'd like to share on this matter?

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
Direct:    701. 280.8591
[email protected]


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to