Bobby,

Check the Georgia code amendments.  Years ago, when I lived in Atlanta, they 
allowed re-using heads in some circumstances.


Eric J. Shelton, PE
Senior Fire Protection Engineer
Associate

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
 
v: (804) 521.7105 f: (804) 217.8520
http://www.haengineers.com


 Do you really need to print this e-mail?



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby McCullough
Sent: Thursday, July 09, 2009 10:22 AM
To: [email protected]
Subject: RE: Heads

So... an inspection at a prison facility finds 20 institutional sidewall 
sprinklers painted or corroded.  New sprinklers should be installed.  These as 
well as the other 80 sidewall sprinklers in the cell block were installed 
incorrectly: they were tightened a quarter turn too far, placing the deflector 
in the vertical position rather than the horizontal position.  

I don't like the idea of "loosening" the sprinklers a quarter turn to get the 
orientation correct.  They could very well leak or the "resistant" nature of 
the sprinkler could be compromised.

Based on NFPA I can't pull the sprinkler out and re-install it, right?

Sounds like the proposal will be for new sprinklers everywhere.

Any ideas?

Bobby McCullough


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of larryshulman
Sent: Wednesday, July 08, 2009 9:03 PM
To: [email protected]
Subject: RE: Heads

NFPA 13-07:
6.2.1 General.   Only new sprinklers shall be installed. 
6.1.2.2   Reconditioned sprinklers shall not be permitted to be utilized on
any new or existing system.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay Jay
Blocker
Sent: Wednesday, July 08, 2009 4:49 PM
To: [email protected]
Subject: Heads

Is there some where written that says you cant reinstall the heads after
removal?  I am coming up blank in my search on this old rule.  

JB


      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to