I saw an aircraft hangar once that had 8" bulk mains hung from this light 
weight construction.  The sprinkler contractor and structural engineer put 
their heads together before hand.  The result was strut channel trapezes spaced 
8 ft apart and spanning four z-purlins.  

The real headache comes when there is no engineer and the GC buys a 
pre-engineered building from a building company who says the warranty is void 
if you hang anything from the purlins. 

J. Scott Mitchell, P.E.

--- On Tue, 7/14/09, [email protected] <[email protected]> wrote:

From: [email protected] <[email protected]>

It's very well possible.   It all depends on the size and gauge of the 
structural member.  More and more installations are using pre-engineered 
buildings which are typically of a light weight construction and not really 
designed for much static loading from the steel.  

Craig L. Prahl, CET   
Fire Protection Specialist




      