All of the obstruction issues were addressed 3 years ago and FM 
signed off on it. They dropped some significant coin to move bridging 
and some ductwork. I have no idea where this is coming from. The 
report should be interesting.


At 07:39 AM 7/20/2009, you wrote:
>Could be there are obstruction issues? Easier to change heads than move
>installed piping in occupied warehouse.
>
>Not everyone seems to understand bridging, HVAC, joist clearances, etc.
>despite the availability of FM's guidelines.
>
>glc
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Monday, July 20, 2009 7:16 AM
>To: [email protected]
>Subject: FM ESFR replacement?
>
>I am working with a company that has an ESFR warehouse previously
>approved by FM. Now, according to them, FM made a recommendation to
>remove the ESFR heads and replace them with K14 control mode
>sprinklers. I'm trying to get a copy of the report. Anybody run into
>this before? Any idea why they would suggest this?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)