There is a reason, but without details of the conditions (occupancy, building construction, water supply, etc.), it is impossible to pinpoint why FM Global made the recommendation. The installation rules for suppression mode sprinklers are very specific, and apparently something changed since their acceptance by FM Global three years ago or was missed back then that made these sprinklers a bad fit now. You'll need to look at Data Sheets 2-2 and 8-9 to figure it out, or call and ask them.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Monday, July 20, 2009 5:24 AM To: [email protected] Subject: RE: FM ESFR replacement? All of the obstruction issues were addressed 3 years ago and FM signed off on it. They dropped some significant coin to move bridging and some ductwork. I have no idea where this is coming from. The report should be interesting. At 07:39 AM 7/20/2009, you wrote: >Could be there are obstruction issues? Easier to change heads than move >installed piping in occupied warehouse. > >Not everyone seems to understand bridging, HVAC, joist clearances, etc. >despite the availability of FM's guidelines. > >glc > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Todd Williams >Sent: Monday, July 20, 2009 7:16 AM >To: [email protected] >Subject: FM ESFR replacement? > >I am working with a company that has an ESFR warehouse previously >approved by FM. Now, according to them, FM made a recommendation to >remove the ESFR heads and replace them with K14 control mode >sprinklers. I'm trying to get a copy of the report. Anybody run into >this before? Any idea why they would suggest this? > Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)