I have a government project with a spec calling for a "Low Air Pressure
Alarm Device" and want to pick the forum's brain to see if they have run
across this before.  They want box with a buzzer and green (all ok), red
(low air pressure), and amber (silence switch on) lights connected to a low
air pressure switch.  See end of email for the exact language.

I found a product that is close to the spec, but missing an amber light at
http://www.modsafe.com/low%20pressure%20warning.htm .  Priced at $500 not
the most economical option either.  Might just have the electrician put some
parts together.

-- 
Regards,
Mark Gouveia

2.7.4 Low Air Pressure Alarm Device
Each dry pipe valve trim shall be provided with a local alarm device
consisting of a metal enclosure containing an alarm horn or bell, silence
switch, green power-on light, red low-air alarm light and amber trouble
light. The alarm device shall be activated by the low air pressure switch.
Upon reduction of sprinkler system pressure to approximately 10 psig above
the dry valve trip point pressure, the low air pressure switch shall
actuate the audible alarm device and a red low-air alarm light.
Restoration of system pressure shall cause the low-air alarm light to be
extinguished and the audible alarm to be silenced. An alarm silence switch
shall be provided to silence the audible alarm. An amber trouble light
shall be provided which will illuminate upon operation of the silence
switch and shall be extinguished upon return to its normal position.