Mark, The government is in a unique position to not limit competition by naming specific manufacturers of specialty items,particularly if the desired item is only made by one manufacturer.They get around this by writing a specification that can ONLY be satisfied by the desired componant.Sounds like a conspiracy theory,but it really isn't.They are just attempting to get what they want and nothing less(they may have their reasons). If possible,try and find a competitor who may have done a similar project with the same branch of the government(GSA,AEC,etc.).If this fails,try and make direct contact with the spec. writer,he may tell you(off the record)where to find it.
Lamar Vaughn,SET McDonough,Georgia ---- Mark Gouveia <[email protected]> wrote: > I have a government project with a spec calling for a "Low Air Pressure > Alarm Device" and want to pick the forum's brain to see if they have run > across this before. They want box with a buzzer and green (all ok), red > (low air pressure), and amber (silence switch on) lights connected to a low > air pressure switch. See end of email for the exact language. > > I found a product that is close to the spec, but missing an amber light at > http://www.modsafe.com/low%20pressure%20warning.htm . Priced at $500 not > the most economical option either. Might just have the electrician put some > parts together. > > -- > Regards, > Mark Gouveia > > 2.7.4 Low Air Pressure Alarm Device > Each dry pipe valve trim shall be provided with a local alarm device > consisting of a metal enclosure containing an alarm horn or bell, silence > switch, green power-on light, red low-air alarm light and amber trouble > light. The alarm device shall be activated by the low air pressure switch. > Upon reduction of sprinkler system pressure to approximately 10 psig above > the dry valve trip point pressure, the low air pressure switch shall > actuate the audible alarm device and a red low-air alarm light. > Restoration of system pressure shall cause the low-air alarm light to be > extinguished and the audible alarm to be silenced. An alarm silence switch > shall be provided to silence the audible alarm. An amber trouble light > shall be provided which will illuminate upon operation of the silence > switch and shall be extinguished upon return to its normal position. > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)