If it's a gvmt. project why would they want local alarm only?

The LAP alarm is supposed to go to a constantly attended location (unless an 
air maint. device is utilized and there is a local low press. alarm).


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Gouveia
Sent: Tuesday, August 11, 2009 1:28 PM
To: [email protected]
Subject: Low Air Pressure Alarm Device - Gov't Project

I have a government project with a spec calling for a "Low Air Pressure Alarm 
Device" and want to pick the forum's brain to see if they have run across this 
before.  They want box with a buzzer and green (all ok), red (low air 
pressure), and amber (silence switch on) lights connected to a low air pressure 
switch.  See end of email for the exact language.

I found a product that is close to the spec, but missing an amber light at 
http://www.modsafe.com/low%20pressure%20warning.htm .  Priced at $500 not the 
most economical option either.  Might just have the electrician put some parts 
together.

--
Regards,
Mark Gouveia

2.7.4 Low Air Pressure Alarm Device
Each dry pipe valve trim shall be provided with a local alarm device consisting 
of a metal enclosure containing an alarm horn or bell, silence switch, green 
power-on light, red low-air alarm light and amber trouble light. The alarm 
device shall be activated by the low air pressure switch.
Upon reduction of sprinkler system pressure to approximately 10 psig above the 
dry valve trip point pressure, the low air pressure switch shall actuate the 
audible alarm device and a red low-air alarm light.
Restoration of system pressure shall cause the low-air alarm light to be 
extinguished and the audible alarm to be silenced. An alarm silence switch 
shall be provided to silence the audible alarm. An amber trouble light shall be 
provided which will illuminate upon operation of the silence switch and shall 
be extinguished upon return to its normal position.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to