Just to ensure we clarify "for all intents and purpose"  I assume you  
mean the 50 psi caveat for systems greater than 5,000 sf kills the use  
of pipe schedule?  I ask since many inaccurately believe that PS is  
not ALLOWED beyond 5,000 SF.

Roland

On Aug 26, 2009, at 7:05 PM, Cliff Whitfield wrote:

> I don't think they were 'required' until sometime (I think '96) when  
> they
> took the pipe schedule option out of the standard (for all intents and
> purposes).  Until then, calcs were allowed but not required since  
> the pipe
> schedule system was still an option.  .
>
>
>
> Cliff
>