Attempting to exclude protection from interior platforms is not  
supported by NFPA 13 unless one reads only the title and ignores the  
text within 8.15.6

Roland

On Sep 8, 2009, at 10:24 AM, Thom McMahon wrote:

> Where would the "Wind borne debris" come from for an interior  
> platform?
> Crawl spaces loading docks and platforms all could collect wind borne
> debris, but I wouldn't think an interior platform would.
>
> Yes 11.2.3.1.4 does say when you need to use the 3000 SF design area
> Adjacent  to these areas, but it does not say that the interior  
> platform is
> anything other than a concealed combustible space.
>
> Thom McMahon, SET

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to