I certainly agree that a skylight is a type of ceiling pocket but when  
you use them interchangeably, it's a problem.   There are significant  
differences in the criteria (most notable being no height limits nor  
material restriction for the covers in skylights). Like apples and  
oranges are both fruits but if you're making a pie, I wouldn't use  
them together.

The 2010 ed. also made some significant changes.

sprinklers in the lower ceiling elevation when the higher ceiling  
elevation is within 12 in. of the deflectors or greater for sprinklers  
with greater listed
distances from the higher ceiling should not be considered unprotected  
ceiling pockets.
A.8.6.7.2(4) It is the intent of this section to allow compartments  
with multiple pockets, where the cumulative volume of the pockets  
exceeds 1000 ft3 and
separated from each other by 10 ft or more and still be permitted to  
be unprotected because with these values, a sprinkler would be  
required between
such pockets. For smaller pockets where the cumulative volume does not  
exceed 1000 ft3, there is no reason to separate the pockets by any  
specific
distance because they are not worse than a single pocket that is 1000  
ft3.

Roland


On Sep 22, 2009, at 6:04 PM, Frans Stoop wrote:

> Roland,
>
> Thanks for your guidance.
> However, with all respect, I disagree about the mix-up.
> According to 8.5.7 a sky light is a ceiling pocket, considering the
> wording "sky lights and similar ceiling pockets".
> (A sky light is a ceiling pocket, but not every ceiling pocket is a  
> sky light.)
>
> This is how I see it:
> In the case of the hall in concern we have Standard Upright Spray
> Sprinklers (chapter 8.6) and sky lights (= ceiling pockets) less than
> 914 mm deep.
> Ergo: section 8.6.7 applies and if the 7 conditions are met par.
> 8.6.7.2 applies too.
> All sprinklers in the hall are QR sprinklers. The sky lights are less
> than 914 mm deep.
> Each sky light is less than 4.5 m3. Every 5 or 6 sky lights make up a
> cluster. Spacing between the sky lights within a cluster is approx. 1
> m. Each cluster is less than 28.3 m3. Spacing between clusters is
> more than 3.05 m.
> The covers are all safety glass.
>
> Your comparison of a smoke/heat vent with a plastic cover was
> enlightening for me.
> Indeed, size matters.
>
> Frans Stoop

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to