Regarding the code or standard on which you base the inspection, I'm speaking 
from my understanding of Georgia regulations and the inspection being done from 
the applicable portions of NFPA 25, 2002.  The Inspector (NICET Level 3 in GA) 
has to be meticulous and methodical to do it right.  Inferring the inspection 
must comply with any portion of IFC (2006 in GA) opens a really big can of 
worms.  I don't believe it is the intent for ITM contractors to inspect based 
on the IFC.  A fire official can and should enforce replacing recalls.
 
For non-compliant and impaired systems, GA regulations require the inspection 
report be sent to the local AHJ.  I send it approximately 7 days after the 
owner has a copy and has had a chance to reply.  If I send information to the 
AHJ which does not originate from the NFPA 25 inspection, I'm going beyond what 
my customer paid me to do, and the intent of the 25 inspection.  And, as I've 
heard a dozen times in seminars, courts may use this against me in the case of 
a loss.
 
Georgia intended to adopt the 2008 edition before now, but with the budget 
crunch the adoption date is unknown.  Once 2008 (or whatever is next) is 
adopted, you can bet the AHJs will see recalled sprinklers in the report.
 
Bobby McCullough
Atlanta Sprinkler Inspection

________________________________

From: sprinklerforum-boun...@firesprinkler.org on behalf of John Drucker
Sent: Fri 9/18/2009 1:18 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Chewable topic.....Omegas



Barry, Pete,

I'm in the process of looking up the exact statutes however it goes without
saying that a certified contractor, as is required in New Jersey, would be
remiss and perhaps fall within the Duty to Act Statute if he/she knowingly
and or should have known but failed to act, i,e, notify the building owner
and fire official. Duty to Act transgressions are considered criminal acts.

I have one in process right now where a diligent fire sprinkler service
provider notified the property owner in writing and copied same to our
office. The end result the citation was issued to the property owner who
authorized the provider to replace some 300 sprinklers. The work starts this
coming Monday along with the requisite fire watch while the system is
impaired.

It comes down to doing the right thing despite the shortcomings of the
reference standard.

John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Maag, Barry
Sent: Friday, September 18, 2009 1:07 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Chewable topic.....Omegas

I haven't been following this thread closely. I am not sure if this has
been mentioned or not. IFC 2006 reads as follows.

901.9 Recall of fire protection components. Any fire protection system
component regulated by this code that is the subject of a voluntary or
mandatory recall under federal law shall be replaced with approved,
listed components in compliance with the referenced standards of this
code. The fire code official shall be notified in writing by the
building owner when the recalled component parts have been replaced.

With that being said I believe that the fire code official should be
notified so that they can enforce the code (law).


Barry Maag

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Forest
Wilson
Sent: Friday, September 18, 2009 11:54 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Chewable topic.....Omegas

The Inspection Forms from the NFSA have a section for noting recalled
components.
I note them and send a certified letter, copying the Fire Marshal.
There is a moral obligation to report recalled heads and what point is
there in doing a main drain test in a school or nursing home if all the
sprinklers are recalled?
The AHJ mentioned previously that allows recalled heads to save the
owner money should consider the night club fires. The inspectors went
to jail.


Forest Wilson

Project Manager
Cherokee Fire Protection Co.
3195 Dayton Xenia Rd Ste 900
Dayton OH 45434

ph: 937-376-2333
fx: 614-455-4324
cell: 937-307-5647


.




Visit our blog: www.cherokee-
fire.blogspot.com







NOTICE: The information contained in this email is intended to be
solely for the use of the named individual or entity to which it is
directed and may contain information that is privileged or otherwise
confidential. It is not intended for transmission to, or receipt by,
anyone other than the named addressee (or a person authorized to
deliver it to the named addressee). It should not be copied or
forwarded to any unauthorized persons. If you have received this
electronic mail transmission in error, please delete it from your
system without copying or forwarding it, and notify the sender of the
error by reply email or by calling Cherokee Fire Protection Co. at
888-347-3079 toll free.


-----Original Message-----
From: George Church <for...@ptd.net>
To: sprinklerforum@firesprinkler.org
Sent: Fri, 18 Sep 2009 11:55:48 -0400
Subject: RE: Chewable topic.....Omegas

The liabilities we ITM contractors can inadvertently inherit are HUGE
and
especially so when you look at the minimal amount of revenue we get for
taking on this risk.

The #25 committee has done a good job of understanding and limiting it
for
us, but contractors doing ITM MUST understand what you can and cannot
put on
an inspection form. The standard means of addressing items outside the
scope
of #25 but relevant is, as Bobby mentioned, a letter (certified makes
sense)
to the owner SEPARATE from the ITM report(s). We inspect buildings as an
agent of the OWNER and if you go outside that contractual relationship,
you
can end up paying dearly for it.

We're putting 100,000 SF retail complex back in service after 10+ years
of
being turned off. It came to the BCO's attn when a spkr guy doing a
small
fit-out discovered the system was off, and rather than advise the
Owner, he
called in the BCO. I assume the spkr guy was working for a GC, and don't
know if the GC was working for the tenant or the Owner. But the Owner's
rep
got a certified letter with a Notice to Vacate in 10 days, called us to
handle it, and from what I heard back from my foreman on site, the
original
spkr guy not only didn't get the service work we ended up with, but he
got
booted off the fit-out, too. I'm not privy to much else and don't really
care- we're doing between 10 and 20 years of tenant improvements,
backflows
on all risers (was a tank and pump; had city run in, connected, but not
placed in service 2 yrs ago), and whatever else may come up. Plus the
chances of the original sprinkie getting additional work is slim, but
they're very happy with us. We were able to get him a 60 day
continuance on
the Vacate Notice within 3 days of the initial call, so the new FA
system
has time to get installed before the revised deadline.

Another reason mandatory ITM by the AHJ isn't such a bad idea. 100k
retail
complex with no working AS, no FA, no smokes, pulls, nada zip. Can't
say the
Owner was right, but glad we were able to a) help him out and b) 3 or
400
labor hrs of work in a bad economy.

glc

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Larrimer,
Peter A (CEOSH)
Sent: Friday, September 18, 2009 10:41 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Chewable topic.....Omegas

That's great John, the way NFPA 25 has been rewritten, the ITM folks are
not obligated to tell (and evidently some teaching out there is actually
discouraged them from telling) the owner that they have recalled Omegas
in their building for fear of getting sued.

Won't get many replaced even with you requesting an official copy of the
NFPA 25 report from the Owner.  Something's broke there don't you think?

Peter Larrimer, PE
Dept. of VA


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John
Drucker
Sent: Friday, September 18, 2009 10:32 AM
To: sprinklerforum@firesprinkler.org
Subject: FW: Chewable topic.....Omegas

While we're sharing jurisdiction info,

As adopted by the NJ Uniform Fire Code, N.J.A.C. 5:70-3, 901.9 & 901.6.2

901.9 Recall of fire protection components.
Any fire protection system component regulated by this code that is the
subject of a voluntary or mandatory recall under federal law shall be
replaced with approved, listed components in compliance with the
referenced
standards of this code. The fire code official shall be notified in
writing
by the building owner when the recalled component parts have been
replaced.

901.6.2 Records.
Records of all system inspections, tests and maintenance required by the
referenced standards shall be maintained on the premises for a minimum
of
three years and shall be copied to the fire code official upon request.

John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby
McCullough
Sent: Friday, September 18, 2009 7:26 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Chewable topic.....Omegas

Georgia requires inspection reports to go to the AHJ.  We are still
under 25-2002, so including a recalled sprinkler is outside the scope of
25.  The AHJ may make the owner change the sprinklers, but until the
state adopts the 2008 standard I'm leaving recalls off reports.
Listening to the AFSA web seminar yesterday reinforced the concept of
keeping a 25 report strictly on 25 issues.

We occasionally find Omegas and inform the owner outside the 25 report.
The certified letter sounds like a better way to go.

Sending reports to insurance companies sounds like a good plan.
Enforcement would be tough.  I've heard from AHJs in the metro area they
receive very few inspection reports and, to my knowledge, enforcement is
sparse.

Bobby McCullough
Atlanta Sprinkler Inspection


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Forest
Wilson
Sent: Thursday, September 17, 2009 5:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Chewable topic.....Omegas

Some states, such as Illinois and Florida require copies of Inspection
Reports to be sent to the AHJ.
If the owner gets upset because the Fire Marshal is informed of
recalled heads then the owner is not the ideal customer anyway.
The AFSA had a guidline on how contractors should deal with recalled
heads uncovered during an inspection and I believe it recommended
sending a certified letter to the owner informing him of the presence
of recalled heads.
What I do is send the letter and copy the Fire Marshal.
Fortunately contractors in states like Illinois and Fla have a legal
obligation to copy the Fire Marshal and the owner can't legally
complain when its done.
The NFPA 25 Committee has considered requiring inspection reports to be
ent to the Insurance Company but has not reached agreement on that
proposal. Local and state requirements to send reports to the AHJ have
the same effect of helping to ensure that deficiencies are repaired.

Forest Wilson

Project Manager
Cherokee Fire Protection Co.
3195 Dayton Xenia Rd Ste 900
Dayton OH 45434

ph: 937-376-2333
fx: 614-455-4324
cell: 937-307-5647


.



Visit our blog: www.cherokee-fire.blogspot.com



-----Original Message-----
From: Thom McMahon <tmcma...@firetechinc.com>
To: sprinklerforum@firesprinkler.org
Sent: Thu, 17 Sep 2009 14:48:53 -0600
Subject: RE: Chewable topic.....Omegas

Once more we are put in the position of "Sprinkler Police" for the fire
marshal and fire inspectors by the IFC. If we report Omega
installations to
the fire marshal, how happy is the owner with us? If we simply tell the
owner he is supposed to tell the fire marshal, and he doesn't what
liability
does that give us? How long are we allowed to ignore the owners failure
to
do what's "required"?

Doesn't much matter which route you chose, if the building has a fire
before
the replacement is done you'll be making an appearance in court.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926




_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to