>Just curious, for a LH at 0.10/1,500 how did you get to 11,000 gallons?

Sloped ceiling and extra sprinklers due to configuration. Demand about 360 gpm







>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Tuesday, September 22, 2009 4:41 PM
>To: [email protected]
>Subject: draft line from suction tank.
>
>I am working on a project with a small pump and a buried suction 
>tank. The design was based on sprinkler demand alone since there are 
>no hydrant connections on the system. Now the local AHJ has come 
>back and says he wants a draft line on the tank. The sprinkler 
>system will take approximately 11000 gallons in the 15000 gallon 
>tank. He claims he would only use it if the pump failed to start. 
>Being this is a rural department in an area with no public water 
>supply, I have a bit of a problem believing this. If I had to 
>include a hose demand from a draft line on a tank, would the 
>standard hose demand be practical?
>The building is all LH and the hose demands would be 100 gpm.
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to