What I've heard from my SOCAL friends, is that they usually install the
storage in the parking garage as you suggest, but also put the pump down
there, eliminating the "Draft" issue. 
Am I describing this correctly Mr. Leyton?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of R Richardson
Sent: Wednesday, September 23, 2009 7:19 AM
To: [email protected]
Subject: RE: draft line from suction tank.



This issue came up here with respect to secondary water tanks required for
high rise buildings in seismic zones.

There was significant resistance from the "building owner community" for two
main reasons.

Firstly, there is a limit to how much negative draft is feasible, which
results in a prohibition of placing the tanks deep down in the underground
parking, which is where the architects typically desire to locate the tank.


The second reason for resistance is the fact that the tank requirement is
based on the premise that a seismic event disabled the city water supply.
The owners were not happy with the possibility that the emergency water for
their fire sprinkler system (plus hose use) would be used for someone else's
building, leaving their building now unprotected. 

We ended up not requiring the draft line.

Probably quite a bit different scenario than what you are involved in, but
something to consider.

Rich Richardson
Seattle Fire Department


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to