Or get acceptance of a water curtain with closed heads 6' o/c, .3/ft, calc #
hds along the length = to 1.2 x MRA?

Right or wrong, let them direct YOU in writing and I'd push for the water
curtain compared to the cost of the WS and the existence of mullions anyway.
Assume you're trying to redeem a bit based on std heads indicated.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Wednesday, September 23, 2009 8:15 AM
To: [email protected]
Subject: RE: Water curtains for windows

What we found was 7.7.8.1 in 2002, current code for AHJ and project. This is
directing us to the use of listed window sprinklers - however this is also
under 7.7 which is Outside Sprinklers for Protection Against Exposure Fires.
(Also located under this heading in 2007 but its 7.8.8.4 with changes) There
is no true direction for this as these windows are inside separating two
areas, the engineer shows standard spray pendent sprinklers but with no
direction the only way to do it correctly (in my opinion) is utilize the
listed window sprinkler. Next battle w/engineer - they have horizontal
mullions and the sprinkler is not listed for windows with horizontal
mullions. They can either change the window style and remove these or remove
the sprinklers and fire rate the glass. 

Oh well, another day....

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Tuesday, September 22, 2009 3:17 PM
To: [email protected]
Subject: RE: Water curtains for windows

Now I'm curious.  What did you find?  I didn't think there was anything
about glass in 13.  What Tim referenced is for vertical openings.  Not
applicable to glass walls. 

There is some stuff in the atrium section of IBC but that's very specific to
atriums and wouldn't apply to other openings. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Tuesday, September 22, 2009 2:51 PM
To: [email protected]
Subject: RE: Water curtains for windows

Nevermind, we found it. Sorry about that...after all it is one of those
days.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Tuesday, September 22, 2009 2:49 PM
To: [email protected]
Subject: Water curtains for windows

It's one of those days. We have a job calling for a water curtain
(sprinklers on both sides of a window), Where is the direction from NFPA for
this? I know TYCO makes a window sprinkler, but isn't there direction for
standard sprinklers in NFPA somewhere? 

 

Thank You,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to