What we found was 7.7.8.1 in 2002, current code for AHJ and project. This is directing us to the use of listed window sprinklers - however this is also under 7.7 which is Outside Sprinklers for Protection Against Exposure Fires. (Also located under this heading in 2007 but its 7.8.8.4 with changes) There is no true direction for this as these windows are inside separating two areas, the engineer shows standard spray pendent sprinklers but with no direction the only way to do it correctly (in my opinion) is utilize the listed window sprinkler. Next battle w/engineer - they have horizontal mullions and the sprinkler is not listed for windows with horizontal mullions. They can either change the window style and remove these or remove the sprinklers and fire rate the glass.
Oh well, another day.... Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Tuesday, September 22, 2009 3:17 PM To: [email protected] Subject: RE: Water curtains for windows Now I'm curious. What did you find? I didn't think there was anything about glass in 13. What Tim referenced is for vertical openings. Not applicable to glass walls. There is some stuff in the atrium section of IBC but that's very specific to atriums and wouldn't apply to other openings. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Tuesday, September 22, 2009 2:51 PM To: [email protected] Subject: RE: Water curtains for windows Nevermind, we found it. Sorry about that...after all it is one of those days. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Tuesday, September 22, 2009 2:49 PM To: [email protected] Subject: Water curtains for windows It's one of those days. We have a job calling for a water curtain (sprinklers on both sides of a window), Where is the direction from NFPA for this? I know TYCO makes a window sprinkler, but isn't there direction for standard sprinklers in NFPA somewhere? Thank You, Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)