I don't know of any exception for the fitter grabbing the hanger 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Monday, September 28, 2009 3:46 PM
To: [email protected]
Subject: RE: 1" Armover and 250 lbs.

TOLCO fig 78 is UL listed for metal deck installation using 1/4 x 1" TEK
screws into 18ga. Metal deck. This would include your 250# plus pipe and
water.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Cyr
Sent: Monday, September 28, 2009 1:00 PM
To: American Fire Sprinkler Association
Subject: 1" Armover and 250 lbs.

Members of the Forum,

Will supporting a 1” armover from a metal deck using a ceiling flange with
1½” tek screws require that the 250 lb load factor be part of the total load
for that hanger?

Does hanging from the horizontal vs. the vertical make a difference if the
support can handle the weight, 30 lb point load? The structural EOR is fine
with it.

I am in need of a NFPA interpretation for the OSHPD (Office of Statewide
Health Planning and Development  -California) representative.

Thanks,
Ed Cyr

Alpha Fire Sprinkler Corp.
San Luis Obispo, CA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to