Hi Thom,I am using the Tolco 78 and its listing allows this application. Do you think this application gets around the NFPA '99, 6-2.1.3 attachment to the vertical part of the decking? A pull test was done and it made it to 300 lbs I think the issue preventing me from using this is the limitation by the SEOR to 50 lbs max on any attachment to the decking. The 250 lb factor is the killer here.
Thanks, Ed On Mon, Sep 28, 2009 at 12:46 PM, Thom McMahon <[email protected]>wrote: > TOLCO fig 78 is UL listed for metal deck installation using 1/4 x 1" TEK > screws into 18ga. Metal deck. This would include your 250# plus pipe and > water. > > Thom McMahon, SET > Firetech, Inc. > 2560 Copper Ridge Dr > P.O. Box 882136 > Steamboat Springs, CO 80488 > Tel: 970-879-7952 > Fax: 970-879-7926 > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Ed Cyr > Sent: Monday, September 28, 2009 1:00 PM > To: American Fire Sprinkler Association > Subject: 1" Armover and 250 lbs. > > Members of the Forum, > > Will supporting a 1” armover from a metal deck using a ceiling flange with > 1½” tek screws require that the 250 lb load factor be part of the total > load > for that hanger? > > Does hanging from the horizontal vs. the vertical make a difference if the > support can handle the weight, 30 lb point load? The structural EOR is fine > with it. > > I am in need of a NFPA interpretation for the OSHPD (Office of Statewide > Health Planning and Development -California) representative. > > Thanks, > Ed Cyr > > Alpha Fire Sprinkler Corp. > San Luis Obispo, CA > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)