Insulation is not adequate to consider the CPVC pipe as being in a  
separate compartment from the attic.

Roland

On Oct 8, 2009, at 7:12 AM, Geoff Dyce wrote:

> Plastic supplying upper floor sprinklers may be run in attics.   
> There is an
> attic sprinkler system also.  If we supply the attic sprinklers from  
> the wet
> system covering the third floor, it appears we must use special  
> application
> sprinklers and these will protect the plastic pipe in the attic.   
> However we
> have a freezing possibility in the attic and will have to run a dry  
> system.
> Assuming the plastic is insulated with lay in insulation, can we use
> standard sprinklers in the attic sprinkler system or will we have to  
> use the
> special application sprinklers anyway.  The issue is of course  
> cost!  Thanks
> in advance.
>
>
>
> Geoffrey H. Dyce
>
> Operations Manager/NICET IV
>
> DELTA Fire Sprinklers, Inc.
>
> A Veteran Owned Small Business
>
> Ph:  407-328-3000 ext 143
>
> Fx:  407-575-9991
>
> E-Mail:  [email protected]
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to