Rather than St Pete, I'm going to bet Roland will be in San Diego with the
rest of the AFSA Convention this coming week- where we'll discuss a lot more
than just this issue. If this particular item isn't covered in a seminar,
there'll be a dozen experts from Tyco and the other mfrs of heads, CPVC, etc
to ask and explore applications in various scenarios......and a few
contractors "in the know". 

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Geoff Dyce
Sent: Friday, October 09, 2009 7:20 AM
To: [email protected]
Subject: RE: attics

Roland and James.  That is it in a nutshell.  Two very good answers and two
contradictions.  Is there a correct answer?  I agree that if there is
exposed plastic in the attic, the Tyco heads are what you need.  From what I
have seen and read, the Tyco attic heads protect the exposed plastic
supplying the attic sprinklers.  I did not see anything regarding insulation
but if the insulation is fire protection for the plastic pipe as Jim says,
why would I have to use the Tyco heads on black pipe supplying the attic
sprinklers if I have no plastic to protect?  Roland....are you going to be
in St Pete this coming week at the seminars?  If you are, lets talk about
this.  Were talking real dollars but we do not want to compromise safety
either.
Geoff

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of James J.
Toth, SET
Sent: Thursday, October 08, 2009 5:42 PM
To: [email protected]
Subject: RE: attics

That depends if your installation needs to meet the requirements of NFPA 13,
NFPA 13R, or NFPA 13D. NFPA 13 is the most stringent and requires full attic
protection and the CPVC piping must be protected. I believe you must use the
special application sprinklers and insulate the pipe in order to meet the
listing requirements.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Thursday, October 08, 2009 4:37 PM
To: [email protected]
Subject: Re: attics

True but I was referring to the question about using spray sprinklers
in the attic and whether CPVC can run below the insulation to supply
the floor below.

Roland

On Oct 8, 2009, at 12:48 PM, James J. Toth, SET wrote:

> Where Tyco attic sprinklers are installed in accordance with their
> listing
> (TYCO document TFP610) the attic piping must be covered with at
> least 6" of
> noncombustible batted insulation at least 24" wide in order to meet
> the
> listing. This insulation is not freeze protection. It is fire
> protection for
> the plastic piping.
>
> Jim Toth
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Roland
> Huggins
> Sent: Thursday, October 08, 2009 12:24 PM
> To: [email protected]
> Subject: Re: attics
>
> Insulation is not adequate to consider the CPVC pipe as being in a
> separate compartment from the attic.
>
> Roland
>
> On Oct 8, 2009, at 7:12 AM, Geoff Dyce wrote:
>
>> Plastic supplying upper floor sprinklers may be run in attics.
>> There is an
>> attic sprinkler system also.  If we supply the attic sprinklers from
>> the wet
>> system covering the third floor, it appears we must use special
>> application
>> sprinklers and these will protect the plastic pipe in the attic.
>> However we
>> have a freezing possibility in the attic and will have to run a dry
>> system.
>> Assuming the plastic is insulated with lay in insulation, can we use
>> standard sprinklers in the attic sprinkler system or will we have to
>> use the
>> special application sprinklers anyway.  The issue is of course
>> cost!  Thanks
>> in advance.
>>
>>
>>
>> Geoffrey H. Dyce
>>
>> Operations Manager/NICET IV
>>
>> DELTA Fire Sprinklers, Inc.
>>
>> A Veteran Owned Small Business
>>
>> Ph:  407-328-3000 ext 143
>>
>> Fx:  407-575-9991
>>
>> E-Mail:  [email protected]
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to