Where Tyco attic sprinklers are installed in accordance with their listing
(TYCO document TFP610) the attic piping must be covered with at least 6" of
noncombustible batted insulation at least 24" wide in order to meet the
listing. This insulation is not freeze protection. It is fire protection for
the plastic piping.

Jim Toth

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Thursday, October 08, 2009 12:24 PM
To: [email protected]
Subject: Re: attics

Insulation is not adequate to consider the CPVC pipe as being in a
separate compartment from the attic.

Roland

On Oct 8, 2009, at 7:12 AM, Geoff Dyce wrote:

> Plastic supplying upper floor sprinklers may be run in attics.
> There is an
> attic sprinkler system also.  If we supply the attic sprinklers from
> the wet
> system covering the third floor, it appears we must use special
> application
> sprinklers and these will protect the plastic pipe in the attic.
> However we
> have a freezing possibility in the attic and will have to run a dry
> system.
> Assuming the plastic is insulated with lay in insulation, can we use
> standard sprinklers in the attic sprinkler system or will we have to
> use the
> special application sprinklers anyway.  The issue is of course
> cost!  Thanks
> in advance.
>
>
>
> Geoffrey H. Dyce
>
> Operations Manager/NICET IV
>
> DELTA Fire Sprinklers, Inc.
>
> A Veteran Owned Small Business
>
> Ph:  407-328-3000 ext 143
>
> Fx:  407-575-9991
>
> E-Mail:  [email protected]
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to