We installed extra FDCs on a place where we'd installed K25 ESFR at 60 PSI-
But there were hydrants with a very strong city supply available nearby.

Yea, if it goes, I'll know 2 counties away from the black smoke. Maybe I
shouldn't send these emails out the week we renew our insurance :)

I understand your dilemma- "we want another one of these". 
I'd just try to make things as obvious as you can as to what is what, and
hopefully relay to the PM that the FDC should come in for a preplan.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Splawn,
Shannon
Sent: Monday, November 02, 2009 3:54 PM
To: [email protected]
Subject: RE: Test header at pump house

They will have private yard hydrants; in fact, lots and lots of them.

"... Especially if, in the background, something is happening in a place
where they'd have the need for 3 FDCs on a 12" manifold- I assume a complex
with a lot of nasties in quanitity. Like those adjacent chem. Plants and
refineries that look like if one goes, there goes Delaware. And NJ and
eastern PA."

You are very close to being right on target.

Shannon Splawn, CFPS
Jacobs
Fire Protection | Mechanical Engineering Dept.
513.674.3822
[email protected]

 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Monday, November 02, 2009 3:53 PM
To: [email protected]
Subject: RE: Test header at pump house

Actually, there is no need for the test header on a fire pump- IF you have
standpipe FHVs, hydrants or other means for testing the flow.

And with a flow meter installed, you only have to flow water and measure it
every -3 yrs? Sorry, I didn't commit #25 to memory, but its less than
annually.

IF you end up with a storz FDC and Storz test header, I'd make signage so
obvious- never mind, it won't matter. They'll hook LDH up to the first storz
they come to and start pumping. Especially if, in the background, something
is happening in a place where they'd have the need for 3 FDCs on a 12"
manifold- I assume a complex with a lot of nasties in quanitity. Like those
adjacent chem. Plants and refineries that look like if one goes, there goes
Delaware. And NJ and eastern PA.

glc



NOTICE - This communication may contain confidential and privileged
information that is for the sole use of the intended recipient. Any viewing,
copying or distribution of, or reliance on this message by unintended
recipients is strictly prohibited. If you have received this message in
error, please notify us immediately by replying to the message and deleting
it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to