It sounds to me that you need to confirm with the owners that that is in fact 
what they really want for the pump test header.  It's a unique enough 
configuration that one would think the owner has a plan for the use of these 
connections as test outlets. Then again, the original design may have been a 
goof-up - either by the owner or the designer.

I would recommend you assume nothing. Verify they have a plan for testing 
through these connections.

As to the validity in relation to NFPA documents - I don't think there is a 
problem, as long as there is a means to actually use these storz connections 
for full-flow testing of the pump.

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104-7079

Direct:    701. 280.8591
Fax:        701.280.8739
Cell:        701.371.5759

[email protected]
www.ulteig.com

Confidentiality Notice
This message may contain privileged and confidential information. If you think, 
for any reason, this message may have been addressed to you in error, you   
must not disseminate copy or take any action in reliance on it, and we would 
ask you to notify me immediately by return email to [email protected].



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Splawn, Shannon
Sent: Monday, November 02, 2009 12:20 PM
To: [email protected]
Subject: RE: Test header at pump house

Each storz has a 6" butterfly control valve.  The plan also includes a flow
meter that is returned to the storage tank.  As I said, this is just me
copying the design done by another for this customer and I've learned not to
question a lot of what was done beforehand...

Shannon Splawn, CFPS
Jacobs
Fire Protection | Mechanical Engineering Dept.
513.674.3822
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to