It certainly does- it gives us the reference pointing out where the
structural engineer of record didn't follow the requirements of the IBC when
designing the steel- if and when we encounter that problem.

It's a perfect qualification to when the AE team attempts to place the onus
on us for structural sufficiency. Simply qualify your bid that you're
assuming the structural EOR met 1606.2 as REQUIRED by the IBC. Then you have
the onus of giving dead loads and point loading at hanger points and let
them complete their compliance with 1606.2 when actual values are available.

Thanks again, John- 

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, November 18, 2009 7:12 AM
To: [email protected]
Subject: RE: Hangers

2006 IBC CHAPTER 16 STRUCTURAL DESIGN

1602.1 Definitions.
The following words and terms shall, for the purposes of this chapter, have
the meanings shown herein.

DEAD LOADS. The weight of materials of construction incorporated into the
building, including but not limited to walls, floors, roofs, ceilings,
stairways, built-in partitions, finishes, cladding and other similarly
incorporated architectural and structural items, and the weight of fixed
service equipment, such as cranes, plumbing stacks and risers, electrical
feeders, heating, ventilating and air-conditioning systems AND FIRE
SPRINKLER SYSTEMS.

1606.2 Design dead load.
For purposes of design, THE ACTUAL WEIGHTS OF MATERIALS OF CONSTRUCTION AND
FIXED SERVICE EQUIPMENT SHALL BE USED. In the absence of definite
information, values used shall be subject to the approval of the building
official.

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
New Jersey


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Tuesday, November 17, 2009 11:26 AM
To: [email protected]
Subject: RE: Hangers

Sounds like the "Toys R Us" roof collapse fiasco to a T.
If structural engineers allow the owner and architect to buffalo them into
designing a structure with NO allowance for or less than "Industry Standard"
allowance for that type of structure for the weight of mechanical systems,
wind or snow/rain loads. They need to get it in writing or walk. Cause when
the roof falls down, everyone is going to turn to them.

My suggestion, if you receive a spec. that requires the fire sprinkler
contractor to verify the ability of the structure to support the fire
sprinkler system. That your request a detailed point load of every other
system including electrical and alarm systems, every seismic load calc,
attachment location, allowable safety factor, maximum allowable deflection
and applied deflection for applied loads and incidental loads such as wind,
snow or rain. Basically make them S*#T paper until you have so much data,
all you can say is "No, in our professional opinion as a fire protection
contractor, we don't believe that this structure will support the additional
loads of the fire sprinkler system, please have the structural engineer
verify that our loads will make this structure unsafe." Give the structural
engineer your drawings and let him do his job.

I know this does not win many friends, but any Arch. That writes this crap
is no-ones friend. Not yours, Not the owners, and not the structural
engineers. 

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, November 16, 2009 3:26 PM
To: [email protected]
Subject: RE: Hangers

Maybe in the perfect world but in reality it won't happen that way.  I've
seen too many value engineered projects where one of the first things to go
is the bldg. structure.  Usually from an engineered bldg to a pre-engineered
spaghetti noodle design that will barely hold itself up and sure isn't
taking into consideration all the utility loading. And forget about EQ
bracing, that would cause someone to have a stroke.  Fortunately none of
these super-econo model designs required bracing.

In today's economy everything is up for grabs, nothing is exempt.


Craig L. Prahl, CET   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to