I would still consider that unsavory, because its based on greed.
Structural steel is one thing that should never be be value engineered.
Using barjoists that will fold like a house of cards when someone hangs a
plant from them isn't very smart in my opinion, and it cheapens the long
term sustainability of construction.  You don't often see issues with
support when working on older buildings because they actually built them to
last.  I feel very sorry for anyone that has to retrofit a Target store in
the next 30-40 years.

The simple solution is to stop trying to save a couple bucks by skimping on
structural steel, or get a fire protection engineer involved much earlier in
the process of the building design.

On Mon, Nov 16, 2009 at 4:54 PM, <[email protected]> wrote:

> Unsavory as a substitute for greed and crook is interesting.  Let's not
> forget ignorance or, more importantly, the ignorance of ignorance.
> Everyone is correct in that the A/E is one of the worst offenders in this
> case as they usually only supply specific technical specifications without
> any really legal language as to who is responsible for all of the spec
> sections and who coordinates them.  Usually, some language may be inferred
> as the General Contractor is responsible.  While this is true, much
> gnashing of teeth occurs before corrections are made.
>
> Case in point is the hanging of large mains on bar joists that are not
> capable of supporting the actual weight of the water filled pipe, much less
> the added 250 #.  This is where reinforcement bracing has to be added to
> the bar joists to support the large pipe.  This is more likely to happen in
> a spec warehouse project, but could certainly occur in an old building that
> was never meant to support the added live load that a large sprinkler
> system presents.  Overall, the entire sprinkler system could be viewed as a
> uniform load, however large mains supported at 12 or 15 foot centers can
> present quite a point load at their support points.
>
> So, who is responsible for this situation?  Who examines the sprinkler
> contractor's shop drawings and determines the loads?  Who determines that
> the supports provided by the sprinkler contractor will be adequate for the
> sprinkler pipe alone?   What happens if the sprinkler system load is added
> to the mechanical chilled water and hot water line load supported by the
> same structural elements?  It would seem that the A/E would have some
> responsibility in this, but he is already out of the picture by the time
> the sprinkler shop drawings are done.
>
> Thank You
>
> Rahe Loftin, P.E.
> Region 7 - GSA
> Office - 817-978-7299
> Fax - 817-978-8644
> Cell - 817-371-3102
>
>
>
>
>
>             Ron Greenman
>             <rongreen...@gmai                                          To
>             l.com>                    [email protected]
>             Sent by:                                                   cc
>             sprinklerforum-bo
>             un...@firesprinkl                                     Subject
>             er.org                    Re: Hangers
>
>
>             11/16/2009 10:10
>             AM
>
>
>             Please respond to
>             sprinklerfo...@fi
>              resprinkler.org
>
>
>
>
>
>
> Unsavory. Nice. That's the kind of word I love to use in lieu of greed
> and crook and the like. Unsavory.
>
> On Mon, Nov 16, 2009 at 7:53 AM,  <[email protected]> wrote:
> > Point being, read the contract and the specs very carefully.  There is
> much ignorance in the AE realm on what the sprinkler contractor is to
> do.  Sometimes it's not all ignorance but just some unsavory persons
> looking for a stooge on which to hang the undesirable or forgotten work.
> >
> >
> > Craig L. Prahl, CET
> > Fire Protection Specialist
> > Mechanical Department
> > CH2MHILL
> > Lockwood Greene
> > 1500 International Drive
> > PO Box 491, Spartanburg, SC  29304-0491
> > Direct - 864.599.4102
> > Fax - 864.599.8439
> > [email protected]
> > http://www.ch2m.com
> >
> >
> > -----Original Message-----
> > From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron
> Greenman
> > Sent: Monday, November 16, 2009 10:48 AM
> > To: [email protected]
> > Subject: Re: Hangers
> >
> > Be careful though because out this way many of the lesser savvy AHJs are
> interpreting this to mean that the sprinkler contractor is responsible for
> proving the building will support the system and so the GCs are learning to
> specify that in their contracts knowing they'll get backing. Some (both GCs
> and AHJs) are even trying to require the sprinkler contractor to upgrade
> the structure if necessary. I have even seen one contract that was trying
> to pin the soils engineering on the sprinkler guy by requiring he verify
> that the dirt work, foundations and structure were adequate. Just last week
> a friend was contractually obligated for $16,000.00 worth of structural
> upgrades even though not a part of the contract because the AHJ wouldn't
> release the sprinkler permit until structural calcs were submitted with the
> plans.
> >
> > On Mon, Nov 16, 2009 at 7:13 AM,  <[email protected]> wrote:
> >> I believe the general consensus the last time this was asked was that
> the requirement you quoted pertained to the hanger not the structure as
> specifying building requirements would be beyond the scope of NFPA 13.
> >>
> >>
> >>
> >> Craig L. Prahl, CET
> >> Fire Protection Specialist
> >> Mechanical Department
> >> CH2MHILL
> >> Lockwood Greene
> >> 1500 International Drive
> >> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
> >> 864.599.8439 [email protected] http://www.ch2m.com
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of Greg
> >> Lindholm
> >> Sent: Monday, November 16, 2009 10:09 AM
> >> To: SprinklerFORUM
> >> Subject: Hangers
> >>
> >> It's Monday and the brain doesn't seem to be working right.
> >>
> >> Section 9.1.1.2 (2002) says that the the hangers shall be designed to
> support the water filled pipe plus 250#. Does the structure itself need to
> support that much, or just the hanger assembly itself.
> >>
> >> Gregory Lindholm
> >> Metro Fire Protection, Inc.
> >> 8693 SE 34th Ave.
> >> Owatonna, MN 55060
> >> 507-451-9694
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]<to%[email protected]>
> >> (Put the word unsubscribe in the subject field)
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]<to%[email protected]>
> >> (Put the word unsubscribe in the subject field)
> >>
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering
> > Bates Technical College
> > Tacoma, WA
> >
> > Member:
> > SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
> _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to