They're most likely talking about using nitrogen cylinders, not nitrogen 
compressors.  Rationale is that the cylinders require no maintenance, no power, 
etc.   Big problem is if you have a leaky system you can deplete the nitrogen 
at the most inopportune moments, (holidays, shutdowns, weekends, middle of the 
night, etc) and then you have a false trip.  It's hard to replace the 
reliability of a local air compressor.

Corrosion is typically not even a thought when it comes to this option, it's 
usually all about $$$$$$$.

Personally I try to dissuade any client from going this route when they bring 
up the idea.

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Wednesday, November 18, 2009 10:26 AM
To: [email protected]
Subject: RE: Nitrogen compressors

Has anyone installed a Nitrogen compressor on a pre-action system? Have a 
series of Data Centers with existing pre-action systems, where the owner is 
requesting Nitrogen to replace air compressors.
They think there is a corrosion advantage? Anyone have any info on that? Can 
MIC survive or grow in a Nitrogen rich environment? I know that nitrogen 
compressors are not "Pure" nitrogen, so is there enough oxygen to feed the MIC?

Any help appreciated.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to