Mark is correct about both aerobic and anaerobic bacteria being
responsible for MIC. The use of nitrogen alone will not prevent MIC.
Nitrogen generators are about 95 percent nitrogen and 5 percent Oxygen.
That is enough oxygen to support both types of bacteria.

Yes nitrogen is dryer than a typical air compressor but there are FM
approved dryer/compressor assemblies that will provide the same level of
dryness for probably less than half the price of a N2 generator.

The use of bottles instead of a generator or a dryer/compressor could be
a bad idea. We have used bottled nitrogen systems in the past for dry
pipe systems and as a pressure source in place of an electric pump for
small wet pipe systems. The problem was leaks in the system would
deplete the N2 tanks. Customers were not happy about having to replace
N2 bottles a few times a year. They blamed us saying they never had
those problems when they used an air compressor. They couldn't
comprehend the limited supply in a bottle vs the ability to generate
more with a compressor.

Regards,

mike

Mike Henke  CET
Sprinkler Product Manager
Potter Electric Signal Co.
www.pottersignal.com
1-800-325-3936

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Phelps,
Mark
Sent: Wednesday, November 18, 2009 11:02 AM
To: [email protected]
Subject: RE: Nitrogen compressors

Some of the microbs responsible for the corrosion refered to as MIC are
aerobic, meaning they require oxygen to exist, others are anarobic
meaning they do not. Anarobic bacteria are some of the oldest lifeforms
on earth and may live in entirely oxygen free enviroments. there ya
havit.
Mark at Aero

-----Original Message-----
From: [email protected]
[mailto:[email protected]]on Behalf Of Thom
McMahon
Sent: Wednesday, November 18, 2009 9:47 AM
To: [email protected]
Subject: RE: Nitrogen compressors


This is the system that is being recommended. NOT compressed Nitrogen
bottles. The reductions they address are for oxygen induced corrosion.
It
would be interesting to know if MIC is still a problem in these systems.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, November 18, 2009 9:30 AM
To: [email protected]
Subject: RE: Nitrogen compressors

Everything you ever wanted to know about Nitrogen Generators:

http://www.fpscmi.com/

Thanks,
Ricky






_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to