We've just added the attic to a R-1 hotel since it required draftstopping
above each corridor wall AND all the party walls between guest rooms- would
have been a nightmare. Plus, its more work for the sprinkies in a bad year-
we'll take it.

GC originally contemplated just the drywall on the truss faces every 3,000
SF which is very simple draftstopping when applied before the truss is
lifted into place....then it grew ugly so it'll be a job for ATTIC
SPRINKLERS :)  

And as my hose valve expert friend points out, it doesn't affect the
interstitial spaces above lower floors, the 4-head MAX calc, .05 density,
etc. that we all know and love about 13R.

I'm thankful my friends like Steve and Bobby DIDN'T die in their respective
motor-related "incidents" and hope everyone gets a chance to enjoy a little
time together with family and a lot of calories.

glc 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of steve
Sent: Wednesday, November 25, 2009 1:07 PM
To: AFSA
Subject: Re: concealed space

On a building of this construction type, there may be value to protecting
the attic with sprinklers in lieu of draft-stopping as prescribed by code;
we've done this on more than just a couple of projects.   And keeping in
mind that it doesn't turn into a 13 design.  It's still 13R, but with the
attic protected per 13 as an "area outside the dwelling units"

Steve L. 


Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "David Blackwell" <[email protected]>
Date: Wed, 25 Nov 2009 09:57:14 
To: <[email protected]>
Subject: RE: concealed space

What George refers to is a very important aspect of the building code 
that may be overlooked.  The architect's design choices can force you to 
use a "higher" standard (NFPA 13 or NFPA 13R) system in the building 
that otherwise falls within the scope of a "lower" standard (NFPA 13R or 
NFPA 13D) system. 
The (2006) IBC Code and Commentary Figure 903.3.1.1 contains a useful 
table for understanding why an architect may specify a higher standard 
than a sprinkler contractor may think is necessary.  
  
David W. S. Blackwell, II, PE, CFI-I, CFPE 
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp
<http://www.llr.state.sc.us/firemarshal.asp>  
---------------------------------------------------------------- 
 
-----Original Message----- 
From: [email protected] 
[mailto:[email protected]
<mailto:[email protected]> ] On Behalf Of George 
Church 
Sent: Wednesday, November 25, 2009 12:20 PM 
To: [email protected] 
Subject: RE: concealed space 
And you can't use 13R under the 2006 IBC if the design team used the 
sprinkler increase in order to build it, you can add a story but the SF 
increase must come from frontage or other, non-sprinkler factors. Doubt 
this 
applies to YOUR building as it could also be under the Int'l Existing 
Building Code. 
I'D BE AMAZED IF A SCHOOL CONVERTED TO APTS IS ABLE TO BE PROTECTED 
APPROPRIATELY BY NFPA 13D !!!!!!!!  We've done 2 schools and a church 
converted to apts in the past year, all 13R. There isn't a lot of 
difference 
in cost to do it correctly (13R) and if you need to, have em add some 8' 
deep lintels where the living room ends and a corridor to bedrooms 
start- 
you'll not have to flow the corridor heads in that calc with the 
living/dining/kitchen area. This can get you down to a 2 or 3 head calc, 
max 
4 in 13R. The little country church ended up as a 2-head flow, a 
challenging 
35 GPM at 30 PSI for a water supply- the developer had to change the 
well 
pump, big deal. 
While you may find something on the AFSA site comparing 13r and 13D, the 
text is available for free reading at www.nfpa.org codes and standards, 
list 
of codes and standards, click on 13r, applicable edition in your 
jurisdiction, and then down at the bottom of the page, click on PREVIEW 
THIS 
DOCUMENT and fill out the questionnaire if you aren't logged in already. 
David offers wise words WRT the IBC impact, although you likely don't 
have 
balconies in a school->apt conversion. 
To ALL my friends on the Forum, best wishes for a thoroughly enjoyable 
thanksgiving respite. 
George Church 
Rowe Sprinkler 
 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
For Technical Assistance, send an email to: [email protected] 
To Unsubscribe, send an email to:[email protected] 
(Put the word unsubscribe in the subject field) 
  
__________ Information from ESET NOD32 Antivirus, version of virus signature
database 4636 (20091125)__________ 
The message was checked by ESET NOD32 Antivirus. 
http://www.eset.com <http://www.eset.com> 
  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to