Yes, and if there is one tap to several buildings then domestic demand fore ALL buildings in the complex needs to be accounted for for EACH hydraulic calc needed.
On Tue, Dec 1, 2009 at 12:11 PM, Eric Tysinger <[email protected]> wrote: > Good afternoon all.. > > I am looking for clarification on when domestic demand is required to be > account for? > > Based on section 6.5.5, domestic demand is required when common domestic/fire > lines are used. What exactly is the definition of common? The commentary in > the handbook goes on to reference figure A.6.5.3(9) which doesn't exist, as > an example of a combined arrangement. Should this A.6.5.3(9) be worded as > A.6.5.3(a)? If this is the case what about figure A.6.5.3(b), in this > situation where the fire and domestic are separate connections, would > domestic demand be required? > > In the situation of a community subdivision where the city main is tapped > once, then the water main runs throughout the project feeding hydrants, > domestic and fire lines, and the same arrangement as figure A.6.5.3(b) is > used, would this require domestic demand to be accounted for? > > Thanks, > Eric Tysinger CET > NICET 108988 > Designer > Wayne Automatic Fire Sprinklers, Inc. > 4370 Motorsport Drive > Concord, NC 28027 > p: (704)782-3032 > f: (704)795-6838 > C: (239)633-9703 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)