You have to assume that the single main line is feeding domestic demand to all buildings when the fire occurs and so the fire demand for the one building is now added to the domestic demand for all buildings, plus hose stream. If you're being fed from a loop then domestic demand for the building in question only.
On Tue, Dec 1, 2009 at 12:20 PM, Eric Tysinger <[email protected]> wrote: > I don't think I agree with all buildings on the site needing to be accounted > for. One building I just recently finished had a domestic demand of 375 gpm, > if there were 5 of these building on the site, I would have to account for > 1875 gpm? That alone exceeds the available flow on many projects I have seen. > > Eric Tysinger > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Ron Greenman > Sent: Tuesday, December 01, 2009 3:12 PM > To: [email protected] > Subject: Re: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook) > > Yes, and if there is one tap to several buildings then domestic demand fore > ALL buildings in the complex needs to be accounted for for EACH hydraulic > calc needed. > > On Tue, Dec 1, 2009 at 12:11 PM, Eric Tysinger <[email protected]> wrote: >> Good afternoon all.. >> >> I am looking for clarification on when domestic demand is required to be >> account for? >> >> Based on section 6.5.5, domestic demand is required when common >> domestic/fire lines are used. What exactly is the definition of common? The >> commentary in the handbook goes on to reference figure A.6.5.3(9) which >> doesn't exist, as an example of a combined arrangement. Should this >> A.6.5.3(9) be worded as A.6.5.3(a)? If this is the case what about figure >> A.6.5.3(b), in this situation where the fire and domestic are separate >> connections, would domestic demand be required? >> >> In the situation of a community subdivision where the city main is tapped >> once, then the water main runs throughout the project feeding hydrants, >> domestic and fire lines, and the same arrangement as figure A.6.5.3(b) is >> used, would this require domestic demand to be accounted for? >> >> Thanks, >> Eric Tysinger CET >> NICET 108988 >> Designer >> Wayne Automatic Fire Sprinklers, Inc. >> 4370 Motorsport Drive >> Concord, NC 28027 >> p: (704)782-3032 >> f: (704)795-6838 >> C: (239)633-9703 >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> For Technical Assistance, send an email to: [email protected] >> >> To Unsubscribe, send an email >> to:[email protected] >> (Put the word unsubscribe in the subject field) >> > > > > -- > Ron Greenman > Instructor > Fire Protection Engineering > Bates Technical College > Tacoma, WA > > Member: > SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)