But...How do you know it's insignificant unless you run numbers? yeah,
I know I can pretty much tell to but when I have an AHJ that won't
accept a hand calc because he doesn't trust it but will happily accept
the same data if I just make an Excel page look like a calc sheet and
then just enter that data because he thinks Excel is inherently a
hydraulics program....And how difficult is it to multiply the flow
points of one building by the number of buildings to get a total? And
remember that this started with the statement that if the total
domestic flow of the complex had to be included then the total flow
was insufficient to support the sprinklers. Somehow I think total flow
of he domestic within the dead end complex just became a significant
factor.

On Tue, Dec 1, 2009 at 4:12 PM, Steve Leyton <[email protected]> wrote:
> I suppose we could if we want to watch multiple sets of eyes glaze over
> and then go dry.
>
> Here's how I see it:  The effect of added flows increases friction loss
> in a single lateral pipe exponentially as the pipe gets smaller.   The
> effect of 15 other units on a calculation for a 16-plex will be very
> impactful when calculating a system that is supplied by a combined 2" or
> 2 1/2" or 3" water service, but the added flows aren't even measurable
> if the line is 8".  I think it's really important that if you're looking
> at a single building/lateral, that the absolute worst case be observed.
> And the figures in 13R for added flows are pretty conservative, most
> would agree.
>
> But looking at an entire site, wouldn't it make sense to follow the same
> criteria as the plumbing engineer did?  That is the person responsible
> for functionality of the water systems - I'll defer to him or her.   I'm
> not suggesting we should go willy-nilly and performance base every
> aspect of every design, but I am trying to draw a distinction between
> calculating the loss of single lateral to a single building system, as
> opposed to a site system that has far greater capacity based on much
> farther-reaching criteria.    You could add the tabled demands of
> several buildings to an 6" or 8" dead-end main before they register more
> than 0.5 PSI loss on the overall site system.   If the site main is
> looped, you can safely take out for the backflow assemblies and just
> calculate back to the POC to that main.
>
> Maybe I'm understating it ... I dunno.
>
> This is MOST DEFINITELY my opinion only and does not represent the NFPA
> or the Technical Committee on Residential Sprinkler systems.   I'm
> pretty sure it doesn't represent Roland or Phil's or Tom's points of
> view either and I may piss off a director or two in the process.   But
> it's been a long day, I've still got a bunch of stuff to do, and I just
> don't have the energy to keep my guard up.
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bill
> Brooks
> Sent: Tuesday, December 01, 2009 3:52 PM
> To: [email protected]
> Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition
> (Handbook)
>
> Steve, your list of design basis considerations do not appear in NFPA 13
> or
> 13R.  Do you think there is a need to address this topic for a future
> edition of these documents?  Does AFSA have a task force that can work
> up a
> set of recommendations?
>
> In my opinion, the water supply requirements are so vague as to be
> unenforceable and could vary significantly from jurisdiction to
> jurisdiction.  How far into the future should we look to determine
> demand as
> is required by NFPA 13?  I normally look to the plumbing/mechanical
> engineer
> for building usage data, but just how deeply do we need to go into a
> city's
> water supply master plan to assess "future demand"?  Do we need to
> maintain
> annual pressure records for each sprinkler system to confirm we don't
> dip
> below our design assumptions?  Should we require a 5-year flow test as
> part
> of an NFPA 25 inspection?
>
> Bill Brooks
>
> William N. Brooks, P.E.
> Brooks Fire Protection Engineering Inc.
> 372 Wilett Drive
> Severna Park, MD 21146-1904
> 410-544-3620
> 410-544-3032 FAX
> 412-400-6528 Cell
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Leyton
> Sent: Tuesday, December 01, 2009 4:06 PM
> To: [email protected]
> Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition
> (Handbook)
>
> I don't disagree with Ron's take, but it may also be prudent to involve
> the project civil engineer.  Private mains serving all demands - fire,
> domestic, irrigation - can be designed and modeled the same way that
> public ones are.   There is a predictable window during each 24 hour
> day, sometimes it's as narrow as 15 minutes, other times widened to 60
> minutes, known as Peak Day Demand (PDD).   When we request a model from
> a water district in lieu of a flow test (a fact of life here in
> perpetually drought-stricken SoCal), it is always run with the specified
> fire flow added to PDD, which generally already exists in the water
> study if they have one.    So ...   contact the project civil engineer
> and ask what they used as a basis for their design.   If they have
> established a PDD, you can accurately model the performance of that
> private main, and flow test back to the point of connection to THAT
> main, and not necessarily the public one.   Be sure that the demands of
> plumbing and irrigation meters (and/or sub-meters) accounted for, as
> well as backflow losses, etc.   Some will argue that's not a prudent
> course of action; our experience has been that it's accurate to a
> fractional percentage of error.
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron
> Greenman
> Sent: Tuesday, December 01, 2009 12:24 PM
> To: [email protected]
> Subject: Re: Domestic Demand Requirements In NFPA 13R, 2002 Edition
> (Handbook)
>
> You have to assume that the single main line is feeding domestic
> demand to all buildings when the fire occurs and so the fire demand
> for the one building is now added to the domestic demand for all
> buildings, plus hose stream. If you're being fed from a loop then
> domestic demand for the building in question only.
>
> On Tue, Dec 1, 2009 at 12:20 PM, Eric Tysinger <[email protected]>
> wrote:
>> I don't think I agree with all buildings on the site needing to be
> accounted for. One building I just recently finished had a domestic
> demand of 375 gpm, if there were 5 of these building on the site, I
> would have to account for 1875 gpm? That alone exceeds the available
> flow on many projects I have seen.
>>
>> Eric Tysinger
>>
>> -----Original Message-----
>> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron
> Greenman
>> Sent: Tuesday, December 01, 2009 3:12 PM
>> To: [email protected]
>> Subject: Re: Domestic Demand Requirements In NFPA 13R, 2002 Edition
> (Handbook)
>>
>> Yes, and if there is one tap to several buildings then domestic demand
> fore ALL buildings in the complex needs to be accounted for for EACH
> hydraulic calc needed.
>>
>> On Tue, Dec 1, 2009 at 12:11 PM, Eric Tysinger <[email protected]>
> wrote:
>>> Good afternoon all..
>>>
>>> I am looking for clarification on when domestic demand is required to
> be account for?
>>>
>>> Based on section 6.5.5, domestic demand is required when common
> domestic/fire lines are used. What exactly is the definition of common?
> The commentary in the handbook goes on to reference figure A.6.5.3(9)
> which doesn't exist, as an example of a combined arrangement. Should
> this A.6.5.3(9) be worded as A.6.5.3(a)? If this is the case what about
> figure A.6.5.3(b), in this situation where the fire and domestic are
> separate connections, would domestic demand be required?
>>>
>>> In the situation of a community subdivision where the city main is
> tapped once, then the water main runs throughout the project feeding
> hydrants, domestic and fire lines, and the same arrangement as figure
> A.6.5.3(b) is used, would this require domestic demand to be accounted
> for?
>>>
>>> Thanks,
>>> Eric Tysinger CET
>>> NICET 108988
>>> Designer
>>> Wayne Automatic Fire Sprinklers, Inc.
>>> 4370 Motorsport Drive
>>> Concord, NC 28027
>>> p: (704)782-3032
>>> f: (704)795-6838
>>> C: (239)633-9703
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>>
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering
>> Bates Technical College
>> Tacoma, WA
>>
>> Member:
>> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4652 (20091201) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4652 (20091201) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to