I suppose we could if we want to watch multiple sets of eyes glaze over
and then go dry.  

Here's how I see it:  The effect of added flows increases friction loss
in a single lateral pipe exponentially as the pipe gets smaller.   The
effect of 15 other units on a calculation for a 16-plex will be very
impactful when calculating a system that is supplied by a combined 2" or
2 1/2" or 3" water service, but the added flows aren't even measurable
if the line is 8".  I think it's really important that if you're looking
at a single building/lateral, that the absolute worst case be observed.
And the figures in 13R for added flows are pretty conservative, most
would agree.

But looking at an entire site, wouldn't it make sense to follow the same
criteria as the plumbing engineer did?  That is the person responsible
for functionality of the water systems - I'll defer to him or her.   I'm
not suggesting we should go willy-nilly and performance base every
aspect of every design, but I am trying to draw a distinction between
calculating the loss of single lateral to a single building system, as
opposed to a site system that has far greater capacity based on much
farther-reaching criteria.    You could add the tabled demands of
several buildings to an 6" or 8" dead-end main before they register more
than 0.5 PSI loss on the overall site system.   If the site main is
looped, you can safely take out for the backflow assemblies and just
calculate back to the POC to that main.  

Maybe I'm understating it ... I dunno.

This is MOST DEFINITELY my opinion only and does not represent the NFPA
or the Technical Committee on Residential Sprinkler systems.   I'm
pretty sure it doesn't represent Roland or Phil's or Tom's points of
view either and I may piss off a director or two in the process.   But
it's been a long day, I've still got a bunch of stuff to do, and I just
don't have the energy to keep my guard up.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill
Brooks
Sent: Tuesday, December 01, 2009 3:52 PM
To: [email protected]
Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)

Steve, your list of design basis considerations do not appear in NFPA 13
or
13R.  Do you think there is a need to address this topic for a future
edition of these documents?  Does AFSA have a task force that can work
up a
set of recommendations?

In my opinion, the water supply requirements are so vague as to be
unenforceable and could vary significantly from jurisdiction to
jurisdiction.  How far into the future should we look to determine
demand as
is required by NFPA 13?  I normally look to the plumbing/mechanical
engineer
for building usage data, but just how deeply do we need to go into a
city's
water supply master plan to assess "future demand"?  Do we need to
maintain
annual pressure records for each sprinkler system to confirm we don't
dip
below our design assumptions?  Should we require a 5-year flow test as
part
of an NFPA 25 inspection?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Tuesday, December 01, 2009 4:06 PM
To: [email protected]
Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)

I don't disagree with Ron's take, but it may also be prudent to involve
the project civil engineer.  Private mains serving all demands - fire,
domestic, irrigation - can be designed and modeled the same way that
public ones are.   There is a predictable window during each 24 hour
day, sometimes it's as narrow as 15 minutes, other times widened to 60
minutes, known as Peak Day Demand (PDD).   When we request a model from
a water district in lieu of a flow test (a fact of life here in
perpetually drought-stricken SoCal), it is always run with the specified
fire flow added to PDD, which generally already exists in the water
study if they have one.    So ...   contact the project civil engineer
and ask what they used as a basis for their design.   If they have
established a PDD, you can accurately model the performance of that
private main, and flow test back to the point of connection to THAT
main, and not necessarily the public one.   Be sure that the demands of
plumbing and irrigation meters (and/or sub-meters) accounted for, as
well as backflow losses, etc.   Some will argue that's not a prudent
course of action; our experience has been that it's accurate to a
fractional percentage of error. 

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
Sent: Tuesday, December 01, 2009 12:24 PM
To: [email protected]
Subject: Re: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)

You have to assume that the single main line is feeding domestic
demand to all buildings when the fire occurs and so the fire demand
for the one building is now added to the domestic demand for all
buildings, plus hose stream. If you're being fed from a loop then
domestic demand for the building in question only.

On Tue, Dec 1, 2009 at 12:20 PM, Eric Tysinger <[email protected]>
wrote:
> I don't think I agree with all buildings on the site needing to be
accounted for. One building I just recently finished had a domestic
demand of 375 gpm, if there were 5 of these building on the site, I
would have to account for 1875 gpm? That alone exceeds the available
flow on many projects I have seen.
>
> Eric Tysinger
>
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
> Sent: Tuesday, December 01, 2009 3:12 PM
> To: [email protected]
> Subject: Re: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)
>
> Yes, and if there is one tap to several buildings then domestic demand
fore ALL buildings in the complex needs to be accounted for for EACH
hydraulic calc needed.
>
> On Tue, Dec 1, 2009 at 12:11 PM, Eric Tysinger <[email protected]>
wrote:
>> Good afternoon all..
>>
>> I am looking for clarification on when domestic demand is required to
be account for?
>>
>> Based on section 6.5.5, domestic demand is required when common
domestic/fire lines are used. What exactly is the definition of common?
The commentary in the handbook goes on to reference figure A.6.5.3(9)
which doesn't exist, as an example of a combined arrangement. Should
this A.6.5.3(9) be worded as A.6.5.3(a)? If this is the case what about
figure A.6.5.3(b), in this situation where the fire and domestic are
separate connections, would domestic demand be required?
>>
>> In the situation of a community subdivision where the city main is
tapped once, then the water main runs throughout the project feeding
hydrants, domestic and fire lines, and the same arrangement as figure
A.6.5.3(b) is used, would this require domestic demand to be accounted
for?
>>
>> Thanks,
>> Eric Tysinger CET
>> NICET 108988
>> Designer
>> Wayne Automatic Fire Sprinklers, Inc.
>> 4370 Motorsport Drive
>> Concord, NC 28027
>> p: (704)782-3032
>> f: (704)795-6838
>> C: (239)633-9703
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4652 (20091201) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4652 (20091201) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to