but it has been addressed because SITE design is outside the scope of  
13R (and 13 for that matter).  13R requires you to include the  
domestic demand if you have a shared main to the individual building.   
Thats because the main is often quite small.  13 does not require  
adding the domestic due to the minimum 6 inch requirement

Roland

On Dec 2, 2009, at 1:57 PM, Ben Young wrote:

> Eric, I responded to your comment to expand on your last statement,  
> not to
> disagree with you.  I agree about the separate connection dilemma in  
> 13R vs
> 13 systems, and wonder why this has never been addressed by the code
> committees before.