but it has been addressed because SITE design is outside the scope of 13R (and 13 for that matter). 13R requires you to include the domestic demand if you have a shared main to the individual building. Thats because the main is often quite small. 13 does not require adding the domestic due to the minimum 6 inch requirement
Roland On Dec 2, 2009, at 1:57 PM, Ben Young wrote: > Eric, I responded to your comment to expand on your last statement, > not to > disagree with you. I agree about the separate connection dilemma in > 13R vs > 13 systems, and wonder why this has never been addressed by the code > committees before. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)