other than a slight case of paranoia that you might be reading it  
wrong, where's the beef?  IT does indeed mean an increase for only the  
DIPA for the occupancy hazard approach and all preaction in storage  
(except ch 13 Misc and Class I-IV < 12ft and Group A plastic < 5ft  
which can be protected per ch 11 thus the occupancy hazard approach in  
all its glory and modifiers including QR reduction and allowed sloped  
ceilings)

Roland

On Dec 3, 2009, at 6:14 AM, <[email protected]> wrote:

> Need clarification:
>
> Based on NFPA 13, 11.2.3.2.5 only DIPA systems require the 30% area  
> increase.  This does not apply to Single or Non-interlocked PA  
> systems.
>
>
> NFPA 13, 2007, 12.5.1 area increase of 30% only applies to preaction  
> systems installed in storage areas.
>
> Correct?
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist