Yeah, I just needed confirmation to make sure I was reading it right since 
someone read 12.5.1 and insisted it applied to ALL preaction systems. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Thursday, December 03, 2009 10:55 AM
To: [email protected]
Subject: Re: Preaction area increase

other than a slight case of paranoia that you might be reading it wrong, 
where's the beef?  IT does indeed mean an increase for only the DIPA for the 
occupancy hazard approach and all preaction in storage (except ch 13 Misc and 
Class I-IV < 12ft and Group A plastic < 5ft which can be protected per ch 11 
thus the occupancy hazard approach in all its glory and modifiers including QR 
reduction and allowed sloped
ceilings)

Roland

On Dec 3, 2009, at 6:14 AM, <[email protected]> wrote:

> Need clarification:
>
> Based on NFPA 13, 11.2.3.2.5 only DIPA systems require the 30% area 
> increase.  This does not apply to Single or Non-interlocked PA 
> systems.
>
>
> NFPA 13, 2007, 12.5.1 area increase of 30% only applies to preaction  
> systems installed in storage areas.
>
> Correct?
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to