The table above does not seem to correspond with the text in the standard. Assuming that the intent is to apply to any situation where you have storage and that requires the use of 286 degree heads and no separation to another non-storage area; this states that you have to use 286 deg heads for 30 feet with a remote area of 2,000 sq ft.
How does this reconcile (or does it) with 11.2.1.2 which states the protection for the higher hazard shall extend 15 feet? Greg McGahan Operations Manager Living Water Fire Protection 1160 McKenzie Road P.O. Box 877 Cantonment, Florida 32533 (850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)