The table above does not seem to correspond with the text in the standard. 
Assuming that the intent is to apply to any situation where you have storage 
and that requires the use of 286 degree heads and no separation to another 
non-storage area; this states that you have to use 286 deg heads for 30 feet 
with a remote area of 2,000 sq ft.

How does this reconcile (or does it) with 11.2.1.2 which states the protection 
for the higher hazard shall extend 15 feet?

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
[email protected]