I get all that. But I assume most of the pressure in a sidewall is for  
throw and not width, how can we justify a significant decrease in  
pressure based on a decrease in width alone?

Sent from my iPhone

On Dec 10, 2009, at 12:14 PM, <[email protected]> wrote:

> What Roland has stated in both posts is correct.Most,if not  
> all,residential sprinklers are listed for 13,13d,and 13r in  
> residential applications.The minimum flow rates indicared in the  
> data is that which is required to generate flow and pressure to  
> achieve the spray pattern indicared.You still must discharge the  
> minimum flow rate (.05 or .10) while at the same time the minimum  
> flow from the table.If you happen to over-flow the head thats  
> o.k.,but you can't flow less than the stated minimum.
>
> Lamar V.
>
>
> ---- Roland Huggins <[email protected]> wrote:
>> agreed but BOTH the listing flow and the 0.1 by the SXL rule must be
>> evaluated as you indicated in your first message.  Look again at the
>> process assigned larger rectangle (16 x 20) for listing and smaller
>> (18.5 x 12) for the SXL. Along with my prior message, the two should
>> resolve the question in your mind.
>>
>> Roland
>>
>> On Dec 9, 2009, at 4:05 PM, Todd - FPDC wrote:
>>
>>> This is a 13 system so a 0.10 is reqd.
>>>
>>> Sent from my iPhone
>>>
>>> On Dec 9, 2009, at 5:26 PM, Roland Huggins
>>> <[email protected]> wrote:
>>>
>>>> first off you are confusing the issue by stating 0.05 gpm/sf since
>>>> these are not density/area sprinklers.  The 0.05 gpm/sf is a  
>>>> minimum
>>>> flow but it is often exceeded by the listed require pressure for a
>>>> evenly assigned rectangle.  AS in your case, the area for the 16  
>>>> x 20
>>>> is 320 requiring only 16 gpm for the non-criterion 0.05 density.   
>>>> You
>>>> identified the listing requires 22 gpm at 27.4 psi.  So where's the
>>>> beef?
>>>>
>>>> Roland
>>>>
>>>> On Dec 8, 2009, at 7:38 AM, Todd Williams wrote:
>>>>
>>>>> I am reviewing a set of plans where the designer used residential
>>>>> sidewall sprinklers in 13 system (6 story apartment bldg). A
>>>>> particular room is 18'6 x 12' and he has a sidewall throwing the
>>>>> 18'6
>>>>> and centered on the 12 ft wall. Since we have to use a 0.10  
>>>>> density,
>>>>> he based his design on 11.2.3.5.2. The listing for the sprinkler  
>>>>> at
>>>>> the 0.05 density (16 x 20 sp) is 22 gpm at 27.4 psi. If we use the
>>>>> 0.10 density times the area as described per 8.5.2.1 (comment  
>>>>> (2) in
>>>>> 11.2.3.5.2), we get 22.2 gpm at 27.9 psi. How can we expect to get
>>>>> twice the density at a an 18.5 ft distance out of the same flow  
>>>>> and
>>>>> pressure by decreasing the width of a room?
>>>>>
>>>>> Todd G. Williams, PE
>>>>> Fire Protection Design/Consulting
>>>>> Stonington, Connecticut
>>>>> www.fpdc.com
>>>>> 860.535.2
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>
>>>>> For Technical Assistance, send an email to:
>>>>> [email protected]
>>>>>
>>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>>>> [email protected]
>>>>> (Put the word unsubscribe in the subject field)
>>>>>
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: [email protected]
>>>>
>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>>> [email protected]
>>>> (Put the word unsubscribe in the subject field)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to:  
>>> [email protected]
>>>
>>> To Unsubscribe, send an email to:Sprinklerforum- 
>>> [email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> [email protected]
>> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to