This is a 13 system so a 0.10 is reqd.

Sent from my iPhone

On Dec 9, 2009, at 5:26 PM, Roland Huggins  
<[email protected]> wrote:

> first off you are confusing the issue by stating 0.05 gpm/sf since
> these are not density/area sprinklers.  The 0.05 gpm/sf is a minimum
> flow but it is often exceeded by the listed require pressure for a
> evenly assigned rectangle.  AS in your case, the area for the 16 x 20
> is 320 requiring only 16 gpm for the non-criterion 0.05 density.  You
> identified the listing requires 22 gpm at 27.4 psi.  So where's the
> beef?
>
> Roland
>
> On Dec 8, 2009, at 7:38 AM, Todd Williams wrote:
>
>> I am reviewing a set of plans where the designer used residential
>> sidewall sprinklers in 13 system (6 story apartment bldg). A
>> particular room is 18'6 x 12' and he has a sidewall throwing the 18'6
>> and centered on the 12 ft wall. Since we have to use a 0.10 density,
>> he based his design on 11.2.3.5.2. The listing for the sprinkler at
>> the 0.05 density (16 x 20 sp) is 22 gpm at 27.4 psi. If we use the
>> 0.10 density times the area as described per 8.5.2.1 (comment (2) in
>> 11.2.3.5.2), we get 22.2 gpm at 27.9 psi. How can we expect to get
>> twice the density at a an 18.5 ft distance out of the same flow and
>> pressure by decreasing the width of a room?
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, Connecticut
>> www.fpdc.com
>> 860.535.2
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> [email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to