I'm going to take a stab at this... It would seem that the 8.3.2.7 dictates the temperature of the sprinkler would need to extend the distance shown in the Appendix table.
Section 11.2.1.2 dictates the density of the sprinkler needs to extend the 15 foot if the remote area is greater than the actual area protected then the adjacent lower density would become the minimum for any sprinklers within the remote area beyond that. So a 20x20 wide high piled storage area surrounded by OHII warehouse would need to provide the storage density to a minimum 35x35 area(20+15), but if the sprinklers used were 286 for the high piled storage, then the higher temperature sprinklers would need to extend to a minimum 50x50 (20+30 assuming a 2000 sq ft remote area) then the sprinklers could be changed to a 200 deg. Right? -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Tuesday, December 08, 2009 8:33 AM To: [email protected] Subject: Table A.8.3.2.7 The table above does not seem to correspond with the text in the standard. Assuming that the intent is to apply to any situation where you have storage and that requires the use of 286 degree heads and no separation to another non-storage area; this states that you have to use 286 deg heads for 30 feet with a remote area of 2,000 sq ft. How does this reconcile (or does it) with 11.2.1.2 which states the protection for the higher hazard shall extend 15 feet? Greg McGahan Operations Manager Living Water Fire Protection 1160 McKenzie Road P.O. Box 877 Cantonment, Florida 32533 (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) -- ExchangeDefender Message Security: Click below to verify authenticity http://www.exchangedefender.com/verify.asp?id=nB8H3Umv007475&[email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)