Note all that Scott and Craig said about codes and physical properties, but FYI 
the 1987 edition of NFPA 30 says for solid pile or palletized storage of metal 
containers greater than 5 gal. up to 3 containers high Class III should be 
0.25/3000 for high temp or 0.25/5000 for intermediate temp sprinklers (Table 
D-4-6.2(a)).  No where near OH2 and dry. 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 




--- On Thu, 12/17/09, Jim Johnston <[email protected]> wrote:


From: Jim Johnston <[email protected]>
Subject: RE: Class III-A Combustible Liquids
To: [email protected]
Date: Thursday, December 17, 2009, 4:53 PM


It was existing at the time, so the hazard was present when originally
installed.  

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: Todd Williams [mailto:[email protected]] 
Sent: Thursday, December 17, 2009 2:44 PM
To: [email protected]
Subject: RE: Class III-A Combustible Liquids

Was the building originally designed for the drum storage? Almost 
sounds like it was supposed to house something else.


At 05:21 PM 12/17/2009, you wrote:
>Unfortunately the person who designed this did it as Ord II and the AHJ
>bought off on it.  I am pretty certain the codes never allowed this hazard
>as Ord II, I just wanted to have some backing since I don't anything (NFPA
>30) prior to 1993.  Nothing like trying to solve someone else's mistake.
>
>Jim Johnston, P.E.
>Fire Protection Engineer
>Inland Fire Protection, Inc
>1100 Ahtanum Road
>Yakima, WA 98903
>Phone 509-248-4471
>Fax 509-248-1180
>[email protected]
>
>
>-----Original Message-----
>From: [email protected] [mailto:[email protected]]
>Sent: Thursday, December 17, 2009 12:25 PM
>To: [email protected]
>Subject: RE: Class III-A Combustible Liquids
>
>OH II, no, don't think so.  Plus you may have issues with extinguishment
>based on water alone since it's SG=.91 and is insoluble.
>
>
>
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Jim Johnston
>Sent: Thursday, December 17, 2009 3:07 PM
>To: [email protected]
>Subject: RE: Class III-A Combustible Liquids
>
>Craig,
>  The liquid is spearmint oil flash point 143 F, the oil is stored in
>non-relieving steel drums.  I have looked at the MSDS sheets and 2008 NFPA
>30 as well as a small section of NFPA 30 - 1993.  I am pretty comfortable
>with requirements of 1993 and 2008 just don't have the backing of what the
>requirements prior to 1993 were?  I just don't see it as Ordinary II?
>
>Jim Johnston, P.E.
>Fire Protection Engineer
>Inland Fire Protection, Inc
>1100 Ahtanum Road
>Yakima, WA 98903
>Phone 509-248-4471
>Fax 509-248-1180
>[email protected]
>
>
>-----Original Message-----
>From: [email protected] [mailto:[email protected]]
>Sent: Thursday, December 17, 2009 11:20 AM
>To: [email protected]
>Subject: RE: Class III-A Combustible Liquids
>
>I've found a lot of chemical protection systems designed per NFPA 13 with
no
>regard to any other Standard.  Using the text in Chapter 5 within the
>various Hazards they base their design solely on the description of
>conditions and words such as "moderate" or "substantial".
>
>Protection of chemicals is in almost all cases beyond the scope of NFPA 13
>alone.  You need MSDS information as we've stated here on many occasions
but
>if you're not comfortable in analyzing chemical properties,
compatibilities,
>extinguishing methodology (other than water), then defer to someone with
the
>expertise.
>
>What can be especially tricky is when various types of chemicals are stored
>in the same area.
>
>
>The questions I'd be asking are how much of this chemical is present,
(there
>are code limitations), in what kind of area does this storage exist,
>(dedicated chemical storage room/control area or out in the open plant
>area), naturally ask for MSDS, you need to know whether it's a polar
solvent
>or hydrocarbon based material, miscibility, etc., etc., etc.  In some cases
>a dry system may not be acceptable and you may have to go to non or single
>interlocked preaction instead.  Lots of variables and lots of codes issues
>to look at in these cases.
>
>
>
>
>****And by the way I don't qualify as one of the old geezers, but I have
>stayed in a Holiday Inn Express on more than one occasion.
>
>
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Jim Johnston
>Sent: Thursday, December 17, 2009 12:42 PM
>To: [email protected]
>Subject: Class III-A Combustible Liquids
>
>Got a design criteria trivial question for some of the more experienced (PC
>for the old geezers, lol).  A system installed in 1992 protecting Class
>III-A Combustible liquids in 55 gallon non-relieving drums stored 3 high
was
>designed as a dry system and to Ordinary II (.20 / 1950).  By today's
>standards NFPA 30 is the applicable code, I assume it was back then too?
>2008 NFPA 30 is drastically different than when the system was designed
back
>then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000 (high
>temp) or 5000 (ordinary temp) this is for water w/o foam.  My assumption is
>the system was designed inadequate back in 1992 just don't have the
>information to justify my statement.  Can any of my fellow comrades help me
>out?
>
>
>
>Thanks in advance.
>
>
>
>Also I hope all of you a very Merry Christmas.
>
>
>
>Jim Johnston, P.E.
>
>Fire Protection Engineer
>
>Inland Fire Protection, Inc
>
>1100 Ahtanum Road
>
>Yakima, WA 98903
>
>Phone 509-248-4471
>
>Fax 509-248-1180
>
>[email protected]
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to