Ok, to make it more confusing, the EC heads I was going to use are UL
Listed as QR for 14x14 (which I need) and SR for 16x16 - which would
mean by increasing the spacing I could use the exact same head?

AND, the FM rating is SR for 14x14...I want to do this right and for the
heads to operate as intended, not trying to cut corners so please reply
if you have basis or experience with this issue.

Greg McGahan

If you have a storage room defined by the EOR as a .222/2,000 remote
area in the back of a retail store with NO separation to the retail area
and you conform to both requirements (15' of the greater hazard and 30'
of 286 deg heads) into the retail space:

Does this lock you out of changing to EC heads in the retail area if the
EC head is listed as QR since you can't use the QR heads in the back?
This is typical Beam and Purlin Construction and I would not consider a
bay as a compartment.

This really stinks if it is true, but am I right?

Also, in A8.4 of the 2010 edition, it says "should" not shall for using
SR and QR in the same compartment.

Thanks as always for your input.


Greg McGahan
Operations Manager
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to