Jim,

I have code sets going back into the 80s. Do you know what edition of
13 is referenced in the 91 UBC 'cause I don't think I have that.
Perhaps 30 is also directly referenced but if not it would be referred
to in 13.

On Thu, Dec 17, 2009 at 4:08 PM, Jim Johnston
<[email protected]> wrote:
> Should be State, but when community is agricultural based and Billy Bob is
> the local elected official anything is possible.
>
> Jim Johnston, P.E.
> Fire Protection Engineer
> Inland Fire Protection, Inc
> 1100 Ahtanum Road
> Yakima, WA 98903
> Phone 509-248-4471
> Fax 509-248-1180
> [email protected]
>
>
> -----Original Message-----
> From: Todd Williams [mailto:[email protected]]
> Sent: Thursday, December 17, 2009 4:03 PM
> To: [email protected]
> Subject: RE: Class III-A Combustible Liquids
>
> Were the Codes set by the State, County or Local authorities?
>
>
> At 06:58 PM 12/17/2009, you wrote:
>>I already tried that approach, the records are archived at the Counties
>>Office the representative from the Fire Marshals office dug thru the files
>>for this facility unfortunately; everything prior to 1996 is gone.  The
>>applicable codes at the time should have been 1991 UBC & UFC.  It's
> possible
>>that this design was applicable at the time?  Again I find that hard to
>>believe that Ord II was acceptable back then?
>>
>>Jim Johnston, P.E.
>>Fire Protection Engineer
>>Inland Fire Protection, Inc
>>1100 Ahtanum Road
>>Yakima, WA 98903
>>Phone 509-248-4471
>>Fax 509-248-1180
>>[email protected]
>>
>>
>>-----Original Message-----
>>From: Scott A. Futrell [mailto:[email protected]]
>>Sent: Thursday, December 17, 2009 3:06 PM
>>To: [email protected]
>>Subject: RE: Class III-A Combustible Liquids
>>
>>Your research needs to include the Building and Fire Code enforceable at
>>the time of the original construction.  That will tell you what it
>>should have been designed to, whether it was or wasn't won't be known
>>until you start there.  Chris C. had a post about the LAW earlier today
>>on another thread and that is the basis for the requirements you are
>>trying to figure out.
>>
>>Scott Futrell
>>
>>(763) 425-1001 Office
>>(612) 759-5556 Cell
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of Jim
>>Johnston
>>Sent: Thursday, December 17, 2009 4:53 PM
>>To: [email protected]
>>Subject: RE: Class III-A Combustible Liquids
>>
>>It was existing at the time, so the hazard was present when originally
>>installed.
>>
>>Jim Johnston, P.E.
>>Fire Protection Engineer
>>Inland Fire Protection, Inc
>>1100 Ahtanum Road
>>Yakima, WA 98903
>>Phone 509-248-4471
>>Fax 509-248-1180
>>[email protected]
>>
>>
>>-----Original Message-----
>>From: Todd Williams [mailto:[email protected]]
>>Sent: Thursday, December 17, 2009 2:44 PM
>>To: [email protected]
>>Subject: RE: Class III-A Combustible Liquids
>>
>>Was the building originally designed for the drum storage? Almost
>>sounds like it was supposed to house something else.
>>
>>
>>At 05:21 PM 12/17/2009, you wrote:
>> >Unfortunately the person who designed this did it as Ord II and the AHJ
>> >bought off on it.  I am pretty certain the codes never allowed this
>>hazard
>> >as Ord II, I just wanted to have some backing since I don't anything
>>(NFPA
>> >30) prior to 1993.  Nothing like trying to solve someone else's
>>mistake.
>> >
>> >Jim Johnston, P.E.
>> >Fire Protection Engineer
>> >Inland Fire Protection, Inc
>> >1100 Ahtanum Road
>> >Yakima, WA 98903
>> >Phone 509-248-4471
>> >Fax 509-248-1180
>> >[email protected]
>> >
>> >
>> >-----Original Message-----
>> >From: [email protected] [mailto:[email protected]]
>> >Sent: Thursday, December 17, 2009 12:25 PM
>> >To: [email protected]
>> >Subject: RE: Class III-A Combustible Liquids
>> >
>> >OH II, no, don't think so.  Plus you may have issues with
>>extinguishment
>> >based on water alone since it's SG=.91 and is insoluble.
>> >
>> >
>> >
>> >
>> >Craig L. Prahl, CET
>> >Fire Protection Specialist
>> >Mechanical Department
>> >CH2MHILL
>> >Lockwood Greene
>> >1500 International Drive
>> >PO Box 491, Spartanburg, SC  29304-0491
>> >Direct - 864.599.4102
>> >Fax - 864.599.8439
>> >[email protected]
>> >http://www.ch2m.com
>> >
>> >
>> >-----Original Message-----
>> >From: [email protected]
>> >[mailto:[email protected]] On Behalf Of Jim
>>Johnston
>> >Sent: Thursday, December 17, 2009 3:07 PM
>> >To: [email protected]
>> >Subject: RE: Class III-A Combustible Liquids
>> >
>> >Craig,
>> >  The liquid is spearmint oil flash point 143 F, the oil is stored in
>> >non-relieving steel drums.  I have looked at the MSDS sheets and 2008
>>NFPA
>> >30 as well as a small section of NFPA 30 - 1993.  I am pretty
>>comfortable
>> >with requirements of 1993 and 2008 just don't have the backing of what
>>the
>> >requirements prior to 1993 were?  I just don't see it as Ordinary II?
>> >
>> >Jim Johnston, P.E.
>> >Fire Protection Engineer
>> >Inland Fire Protection, Inc
>> >1100 Ahtanum Road
>> >Yakima, WA 98903
>> >Phone 509-248-4471
>> >Fax 509-248-1180
>> >[email protected]
>> >
>> >
>> >-----Original Message-----
>> >From: [email protected] [mailto:[email protected]]
>> >Sent: Thursday, December 17, 2009 11:20 AM
>> >To: [email protected]
>> >Subject: RE: Class III-A Combustible Liquids
>> >
>> >I've found a lot of chemical protection systems designed per NFPA 13
>>with
>>no
>> >regard to any other Standard.  Using the text in Chapter 5 within the
>> >various Hazards they base their design solely on the description of
>> >conditions and words such as "moderate" or "substantial".
>> >
>> >Protection of chemicals is in almost all cases beyond the scope of NFPA
>>13
>> >alone.  You need MSDS information as we've stated here on many
>>occasions
>>but
>> >if you're not comfortable in analyzing chemical properties,
>>compatibilities,
>> >extinguishing methodology (other than water), then defer to someone
>>with
>>the
>> >expertise.
>> >
>> >What can be especially tricky is when various types of chemicals are
>>stored
>> >in the same area.
>> >
>> >
>> >The questions I'd be asking are how much of this chemical is present,
>>(there
>> >are code limitations), in what kind of area does this storage exist,
>> >(dedicated chemical storage room/control area or out in the open plant
>> >area), naturally ask for MSDS, you need to know whether it's a polar
>>solvent
>> >or hydrocarbon based material, miscibility, etc., etc., etc.  In some
>>cases
>> >a dry system may not be acceptable and you may have to go to non or
>>single
>> >interlocked preaction instead.  Lots of variables and lots of codes
>>issues
>> >to look at in these cases.
>> >
>> >
>> >
>> >
>> >****And by the way I don't qualify as one of the old geezers, but I
>>have
>> >stayed in a Holiday Inn Express on more than one occasion.
>> >
>> >
>> >
>> >Craig L. Prahl, CET
>> >Fire Protection Specialist
>> >Mechanical Department
>> >CH2MHILL
>> >Lockwood Greene
>> >1500 International Drive
>> >PO Box 491, Spartanburg, SC  29304-0491
>> >Direct - 864.599.4102
>> >Fax - 864.599.8439
>> >[email protected]
>> >http://www.ch2m.com
>> >
>> >
>> >-----Original Message-----
>> >From: [email protected]
>> >[mailto:[email protected]] On Behalf Of Jim
>>Johnston
>> >Sent: Thursday, December 17, 2009 12:42 PM
>> >To: [email protected]
>> >Subject: Class III-A Combustible Liquids
>> >
>> >Got a design criteria trivial question for some of the more experienced
>>(PC
>> >for the old geezers, lol).  A system installed in 1992 protecting Class
>> >III-A Combustible liquids in 55 gallon non-relieving drums stored 3
>>high
>>was
>> >designed as a dry system and to Ordinary II (.20 / 1950).  By today's
>> >standards NFPA 30 is the applicable code, I assume it was back then
>>too?
>> >2008 NFPA 30 is drastically different than when the system was designed
>>back
>> >then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000
>>(high
>> >temp) or 5000 (ordinary temp) this is for water w/o foam.  My
>>assumption is
>> >the system was designed inadequate back in 1992 just don't have the
>> >information to justify my statement.  Can any of my fellow comrades
>>help me
>> >out?
>> >
>> >
>> >
>> >Thanks in advance.
>> >
>> >
>> >
>> >Also I hope all of you a very Merry Christmas.
>> >
>> >
>> >
>> >Jim Johnston, P.E.
>> >
>> >Fire Protection Engineer
>> >
>> >Inland Fire Protection, Inc
>> >
>> >1100 Ahtanum Road
>> >
>> >Yakima, WA 98903
>> >
>> >Phone 509-248-4471
>> >
>> >Fax 509-248-1180
>> >
>> >[email protected]
>> >
>> >
>> >
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >For Technical Assistance, send an email to: [email protected]
>> >
>> >To Unsubscribe, send an email
>>to:[email protected]
>> >(Put the word unsubscribe in the subject field)
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >For Technical Assistance, send an email to: [email protected]
>> >
>> >To Unsubscribe, send an email
>>to:[email protected]
>> >(Put the word unsubscribe in the subject field)
>> >
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >For Technical Assistance, send an email to: [email protected]
>> >
>> >To Unsubscribe, send an email
>>to:[email protected]
>> >(Put the word unsubscribe in the subject field)
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >For Technical Assistance, send an email to: [email protected]
>> >
>> >To Unsubscribe, send an email
>>to:[email protected]
>> >(Put the word unsubscribe in the subject field)
>> >
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >For Technical Assistance, send an email to: [email protected]
>> >
>> >To Unsubscribe, send an email
>>to:[email protected]
>> >(Put the word unsubscribe in the subject field)
>>
>>Todd G. Williams, PE
>>Fire Protection Design/Consulting
>>Stonington, Connecticut
>>www.fpdc.com
>>860.535.2080
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email
>>to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email
>>to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to