I'm sure this is not the only facility around with a less than acceptable design for the sprinkler system.There are still sprinkler contractors and even AHJ's who know nothing about (or choose to ignore) standards,MSDS,OSHA,etc. who are willing to call any building "Ordinary Hazard" (if they install a ceiling it must be light hazard,right??).Until you get all interested parties on board with the idea that this business is serious (Like,somebody could DIE) we will continue to find these problems. Sermon closed.
---- David de Vries <[email protected]> wrote: > Jim: > > The 1991 UFC Table 79.203-C has the same criteria as the 1987 NFPA 30, i.e. > 0.25/3000 and 5000 for high and intermed temp sprinklers respectively. > > I can fax you a copy of the reqs from it if you need it. > > Dave > > David A. de Vries, P.E., CSP > Firetech Engineering Incorporated > > > > --- On Thu, 12/17/09, Jim Johnston <[email protected]> wrote: > > > From: Jim Johnston <[email protected]> > Subject: RE: Class III-A Combustible Liquids > To: [email protected] > Date: Thursday, December 17, 2009, 6:08 PM > > > Should be State, but when community is agricultural based and Billy Bob is > the local elected official anything is possible. > > Jim Johnston, P.E. > Fire Protection Engineer > Inland Fire Protection, Inc > 1100 Ahtanum Road > Yakima, WA 98903 > Phone 509-248-4471 > Fax 509-248-1180 > [email protected] > > > -----Original Message----- > From: Todd Williams [mailto:[email protected]] > Sent: Thursday, December 17, 2009 4:03 PM > To: [email protected] > Subject: RE: Class III-A Combustible Liquids > > Were the Codes set by the State, County or Local authorities? > > > At 06:58 PM 12/17/2009, you wrote: > >I already tried that approach, the records are archived at the Counties > >Office the representative from the Fire Marshals office dug thru the files > >for this facility unfortunately; everything prior to 1996 is gone. The > >applicable codes at the time should have been 1991 UBC & UFC. It's > possible > >that this design was applicable at the time? Again I find that hard to > >believe that Ord II was acceptable back then? > > > >Jim Johnston, P.E. > >Fire Protection Engineer > >Inland Fire Protection, Inc > >1100 Ahtanum Road > >Yakima, WA 98903 > >Phone 509-248-4471 > >Fax 509-248-1180 > >[email protected] > > > > > >-----Original Message----- > >From: Scott A. Futrell [mailto:[email protected]] > >Sent: Thursday, December 17, 2009 3:06 PM > >To: [email protected] > >Subject: RE: Class III-A Combustible Liquids > > > >Your research needs to include the Building and Fire Code enforceable at > >the time of the original construction. That will tell you what it > >should have been designed to, whether it was or wasn't won't be known > >until you start there. Chris C. had a post about the LAW earlier today > >on another thread and that is the basis for the requirements you are > >trying to figure out. > > > >Scott Futrell > > > >(763) 425-1001 Office > >(612) 759-5556 Cell > > > >-----Original Message----- > >From: [email protected] > >[mailto:[email protected]] On Behalf Of Jim > >Johnston > >Sent: Thursday, December 17, 2009 4:53 PM > >To: [email protected] > >Subject: RE: Class III-A Combustible Liquids > > > >It was existing at the time, so the hazard was present when originally > >installed. > > > >Jim Johnston, P.E. > >Fire Protection Engineer > >Inland Fire Protection, Inc > >1100 Ahtanum Road > >Yakima, WA 98903 > >Phone 509-248-4471 > >Fax 509-248-1180 > >[email protected] > > > > > >-----Original Message----- > >From: Todd Williams [mailto:[email protected]] > >Sent: Thursday, December 17, 2009 2:44 PM > >To: [email protected] > >Subject: RE: Class III-A Combustible Liquids > > > >Was the building originally designed for the drum storage? Almost > >sounds like it was supposed to house something else. > > > > > >At 05:21 PM 12/17/2009, you wrote: > > >Unfortunately the person who designed this did it as Ord II and the AHJ > > >bought off on it. I am pretty certain the codes never allowed this > >hazard > > >as Ord II, I just wanted to have some backing since I don't anything > >(NFPA > > >30) prior to 1993. Nothing like trying to solve someone else's > >mistake. > > > > > >Jim Johnston, P.E. > > >Fire Protection Engineer > > >Inland Fire Protection, Inc > > >1100 Ahtanum Road > > >Yakima, WA 98903 > > >Phone 509-248-4471 > > >Fax 509-248-1180 > > >[email protected] > > > > > > > > >-----Original Message----- > > >From: [email protected] [mailto:[email protected]] > > >Sent: Thursday, December 17, 2009 12:25 PM > > >To: [email protected] > > >Subject: RE: Class III-A Combustible Liquids > > > > > >OH II, no, don't think so. Plus you may have issues with > >extinguishment > > >based on water alone since it's SG=.91 and is insoluble. > > > > > > > > > > > > > > >Craig L. Prahl, CET > > >Fire Protection Specialist > > >Mechanical Department > > >CH2MHILL > > >Lockwood Greene > > >1500 International Drive > > >PO Box 491, Spartanburg, SC 29304-0491 > > >Direct - 864.599.4102 > > >Fax - 864.599.8439 > > >[email protected] > > >http://www.ch2m.com > > > > > > > > >-----Original Message----- > > >From: [email protected] > > >[mailto:[email protected]] On Behalf Of Jim > >Johnston > > >Sent: Thursday, December 17, 2009 3:07 PM > > >To: [email protected] > > >Subject: RE: Class III-A Combustible Liquids > > > > > >Craig, > > > The liquid is spearmint oil flash point 143 F, the oil is stored in > > >non-relieving steel drums. I have looked at the MSDS sheets and 2008 > >NFPA > > >30 as well as a small section of NFPA 30 - 1993. I am pretty > >comfortable > > >with requirements of 1993 and 2008 just don't have the backing of what > >the > > >requirements prior to 1993 were? I just don't see it as Ordinary II? > > > > > >Jim Johnston, P.E. > > >Fire Protection Engineer > > >Inland Fire Protection, Inc > > >1100 Ahtanum Road > > >Yakima, WA 98903 > > >Phone 509-248-4471 > > >Fax 509-248-1180 > > >[email protected] > > > > > > > > >-----Original Message----- > > >From: [email protected] [mailto:[email protected]] > > >Sent: Thursday, December 17, 2009 11:20 AM > > >To: [email protected] > > >Subject: RE: Class III-A Combustible Liquids > > > > > >I've found a lot of chemical protection systems designed per NFPA 13 > >with > >no > > >regard to any other Standard. Using the text in Chapter 5 within the > > >various Hazards they base their design solely on the description of > > >conditions and words such as "moderate" or "substantial". > > > > > >Protection of chemicals is in almost all cases beyond the scope of NFPA > >13 > > >alone. You need MSDS information as we've stated here on many > >occasions > >but > > >if you're not comfortable in analyzing chemical properties, > >compatibilities, > > >extinguishing methodology (other than water), then defer to someone > >with > >the > > >expertise. > > > > > >What can be especially tricky is when various types of chemicals are > >stored > > >in the same area. > > > > > > > > >The questions I'd be asking are how much of this chemical is present, > >(there > > >are code limitations), in what kind of area does this storage exist, > > >(dedicated chemical storage room/control area or out in the open plant > > >area), naturally ask for MSDS, you need to know whether it's a polar > >solvent > > >or hydrocarbon based material, miscibility, etc., etc., etc. In some > >cases > > >a dry system may not be acceptable and you may have to go to non or > >single > > >interlocked preaction instead. Lots of variables and lots of codes > >issues > > >to look at in these cases. > > > > > > > > > > > > > > >****And by the way I don't qualify as one of the old geezers, but I > >have > > >stayed in a Holiday Inn Express on more than one occasion. > > > > > > > > > > > >Craig L. Prahl, CET > > >Fire Protection Specialist > > >Mechanical Department > > >CH2MHILL > > >Lockwood Greene > > >1500 International Drive > > >PO Box 491, Spartanburg, SC 29304-0491 > > >Direct - 864.599.4102 > > >Fax - 864.599.8439 > > >[email protected] > > >http://www.ch2m.com > > > > > > > > >-----Original Message----- > > >From: [email protected] > > >[mailto:[email protected]] On Behalf Of Jim > >Johnston > > >Sent: Thursday, December 17, 2009 12:42 PM > > >To: [email protected] > > >Subject: Class III-A Combustible Liquids > > > > > >Got a design criteria trivial question for some of the more experienced > >(PC > > >for the old geezers, lol). A system installed in 1992 protecting Class > > >III-A Combustible liquids in 55 gallon non-relieving drums stored 3 > >high > >was > > >designed as a dry system and to Ordinary II (.20 / 1950). By today's > > >standards NFPA 30 is the applicable code, I assume it was back then > >too? > > >2008 NFPA 30 is drastically different than when the system was designed > >back > > >then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000 > >(high > > >temp) or 5000 (ordinary temp) this is for water w/o foam. My > >assumption is > > >the system was designed inadequate back in 1992 just don't have the > > >information to justify my statement. Can any of my fellow comrades > >help me > > >out? > > > > > > > > > > > >Thanks in advance. > > > > > > > > > > > >Also I hope all of you a very Merry Christmas. > > > > > > > > > > > >Jim Johnston, P.E. > > > > > >Fire Protection Engineer > > > > > >Inland Fire Protection, Inc > > > > > >1100 Ahtanum Road > > > > > >Yakima, WA 98903 > > > > > >Phone 509-248-4471 > > > > > >Fax 509-248-1180 > > > > > >[email protected] > > > > > > > > > > > >_______________________________________________ > > >Sprinklerforum mailing list > > >[email protected] > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > >For Technical Assistance, send an email to: [email protected] > > > > > >To Unsubscribe, send an email > >to:[email protected] > > >(Put the word unsubscribe in the subject field) > > >_______________________________________________ > > >Sprinklerforum mailing list > > >[email protected] > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > >For Technical Assistance, send an email to: [email protected] > > > > > >To Unsubscribe, send an email > >to:[email protected] > > >(Put the word unsubscribe in the subject field) > > > > > >_______________________________________________ > > >Sprinklerforum mailing list > > >[email protected] > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > >For Technical Assistance, send an email to: [email protected] > > > > > >To Unsubscribe, send an email > >to:[email protected] > > >(Put the word unsubscribe in the subject field) > > >_______________________________________________ > > >Sprinklerforum mailing list > > >[email protected] > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > >For Technical Assistance, send an email to: [email protected] > > > > > >To Unsubscribe, send an email > >to:[email protected] > > >(Put the word unsubscribe in the subject field) > > > > > >_______________________________________________ > > >Sprinklerforum mailing list > > >[email protected] > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > >For Technical Assistance, send an email to: [email protected] > > > > > >To Unsubscribe, send an email > >to:[email protected] > > >(Put the word unsubscribe in the subject field) > > > >Todd G. Williams, PE > >Fire Protection Design/Consulting > >Stonington, Connecticut > >www.fpdc.com > >860.535.2080 > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email > >to:[email protected] > >(Put the word unsubscribe in the subject field) > > > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email > >to:[email protected] > >(Put the word unsubscribe in the subject field) > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email to:[email protected] > >(Put the word unsubscribe in the subject field) > > > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email to:[email protected] > >(Put the word unsubscribe in the subject field) > > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, Connecticut > www.fpdc.com > 860.535.2080 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)