Were the Codes set by the State, County or Local authorities?
At 06:58 PM 12/17/2009, you wrote: >I already tried that approach, the records are archived at the Counties >Office the representative from the Fire Marshals office dug thru the files >for this facility unfortunately; everything prior to 1996 is gone. The >applicable codes at the time should have been 1991 UBC & UFC. It's possible >that this design was applicable at the time? Again I find that hard to >believe that Ord II was acceptable back then? > >Jim Johnston, P.E. >Fire Protection Engineer >Inland Fire Protection, Inc >1100 Ahtanum Road >Yakima, WA 98903 >Phone 509-248-4471 >Fax 509-248-1180 >[email protected] > > >-----Original Message----- >From: Scott A. Futrell [mailto:[email protected]] >Sent: Thursday, December 17, 2009 3:06 PM >To: [email protected] >Subject: RE: Class III-A Combustible Liquids > >Your research needs to include the Building and Fire Code enforceable at >the time of the original construction. That will tell you what it >should have been designed to, whether it was or wasn't won't be known >until you start there. Chris C. had a post about the LAW earlier today >on another thread and that is the basis for the requirements you are >trying to figure out. > >Scott Futrell > >(763) 425-1001 Office >(612) 759-5556 Cell > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Jim >Johnston >Sent: Thursday, December 17, 2009 4:53 PM >To: [email protected] >Subject: RE: Class III-A Combustible Liquids > >It was existing at the time, so the hazard was present when originally >installed. > >Jim Johnston, P.E. >Fire Protection Engineer >Inland Fire Protection, Inc >1100 Ahtanum Road >Yakima, WA 98903 >Phone 509-248-4471 >Fax 509-248-1180 >[email protected] > > >-----Original Message----- >From: Todd Williams [mailto:[email protected]] >Sent: Thursday, December 17, 2009 2:44 PM >To: [email protected] >Subject: RE: Class III-A Combustible Liquids > >Was the building originally designed for the drum storage? Almost >sounds like it was supposed to house something else. > > >At 05:21 PM 12/17/2009, you wrote: > >Unfortunately the person who designed this did it as Ord II and the AHJ > >bought off on it. I am pretty certain the codes never allowed this >hazard > >as Ord II, I just wanted to have some backing since I don't anything >(NFPA > >30) prior to 1993. Nothing like trying to solve someone else's >mistake. > > > >Jim Johnston, P.E. > >Fire Protection Engineer > >Inland Fire Protection, Inc > >1100 Ahtanum Road > >Yakima, WA 98903 > >Phone 509-248-4471 > >Fax 509-248-1180 > >[email protected] > > > > > >-----Original Message----- > >From: [email protected] [mailto:[email protected]] > >Sent: Thursday, December 17, 2009 12:25 PM > >To: [email protected] > >Subject: RE: Class III-A Combustible Liquids > > > >OH II, no, don't think so. Plus you may have issues with >extinguishment > >based on water alone since it's SG=.91 and is insoluble. > > > > > > > > > >Craig L. Prahl, CET > >Fire Protection Specialist > >Mechanical Department > >CH2MHILL > >Lockwood Greene > >1500 International Drive > >PO Box 491, Spartanburg, SC 29304-0491 > >Direct - 864.599.4102 > >Fax - 864.599.8439 > >[email protected] > >http://www.ch2m.com > > > > > >-----Original Message----- > >From: [email protected] > >[mailto:[email protected]] On Behalf Of Jim >Johnston > >Sent: Thursday, December 17, 2009 3:07 PM > >To: [email protected] > >Subject: RE: Class III-A Combustible Liquids > > > >Craig, > > The liquid is spearmint oil flash point 143 F, the oil is stored in > >non-relieving steel drums. I have looked at the MSDS sheets and 2008 >NFPA > >30 as well as a small section of NFPA 30 - 1993. I am pretty >comfortable > >with requirements of 1993 and 2008 just don't have the backing of what >the > >requirements prior to 1993 were? I just don't see it as Ordinary II? > > > >Jim Johnston, P.E. > >Fire Protection Engineer > >Inland Fire Protection, Inc > >1100 Ahtanum Road > >Yakima, WA 98903 > >Phone 509-248-4471 > >Fax 509-248-1180 > >[email protected] > > > > > >-----Original Message----- > >From: [email protected] [mailto:[email protected]] > >Sent: Thursday, December 17, 2009 11:20 AM > >To: [email protected] > >Subject: RE: Class III-A Combustible Liquids > > > >I've found a lot of chemical protection systems designed per NFPA 13 >with >no > >regard to any other Standard. Using the text in Chapter 5 within the > >various Hazards they base their design solely on the description of > >conditions and words such as "moderate" or "substantial". > > > >Protection of chemicals is in almost all cases beyond the scope of NFPA >13 > >alone. You need MSDS information as we've stated here on many >occasions >but > >if you're not comfortable in analyzing chemical properties, >compatibilities, > >extinguishing methodology (other than water), then defer to someone >with >the > >expertise. > > > >What can be especially tricky is when various types of chemicals are >stored > >in the same area. > > > > > >The questions I'd be asking are how much of this chemical is present, >(there > >are code limitations), in what kind of area does this storage exist, > >(dedicated chemical storage room/control area or out in the open plant > >area), naturally ask for MSDS, you need to know whether it's a polar >solvent > >or hydrocarbon based material, miscibility, etc., etc., etc. In some >cases > >a dry system may not be acceptable and you may have to go to non or >single > >interlocked preaction instead. Lots of variables and lots of codes >issues > >to look at in these cases. > > > > > > > > > >****And by the way I don't qualify as one of the old geezers, but I >have > >stayed in a Holiday Inn Express on more than one occasion. > > > > > > > >Craig L. Prahl, CET > >Fire Protection Specialist > >Mechanical Department > >CH2MHILL > >Lockwood Greene > >1500 International Drive > >PO Box 491, Spartanburg, SC 29304-0491 > >Direct - 864.599.4102 > >Fax - 864.599.8439 > >[email protected] > >http://www.ch2m.com > > > > > >-----Original Message----- > >From: [email protected] > >[mailto:[email protected]] On Behalf Of Jim >Johnston > >Sent: Thursday, December 17, 2009 12:42 PM > >To: [email protected] > >Subject: Class III-A Combustible Liquids > > > >Got a design criteria trivial question for some of the more experienced >(PC > >for the old geezers, lol). A system installed in 1992 protecting Class > >III-A Combustible liquids in 55 gallon non-relieving drums stored 3 >high >was > >designed as a dry system and to Ordinary II (.20 / 1950). By today's > >standards NFPA 30 is the applicable code, I assume it was back then >too? > >2008 NFPA 30 is drastically different than when the system was designed >back > >then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000 >(high > >temp) or 5000 (ordinary temp) this is for water w/o foam. My >assumption is > >the system was designed inadequate back in 1992 just don't have the > >information to justify my statement. Can any of my fellow comrades >help me > >out? > > > > > > > >Thanks in advance. > > > > > > > >Also I hope all of you a very Merry Christmas. > > > > > > > >Jim Johnston, P.E. > > > >Fire Protection Engineer > > > >Inland Fire Protection, Inc > > > >1100 Ahtanum Road > > > >Yakima, WA 98903 > > > >Phone 509-248-4471 > > > >Fax 509-248-1180 > > > >[email protected] > > > > > > > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email >to:[email protected] > >(Put the word unsubscribe in the subject field) > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email >to:[email protected] > >(Put the word unsubscribe in the subject field) > > > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email >to:[email protected] > >(Put the word unsubscribe in the subject field) > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email >to:[email protected] > >(Put the word unsubscribe in the subject field) > > > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email >to:[email protected] > >(Put the word unsubscribe in the subject field) > >Todd G. Williams, PE >Fire Protection Design/Consulting >Stonington, Connecticut >www.fpdc.com >860.535.2080 >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)