Were the Codes set by the State, County or Local authorities?

At 06:58 PM 12/17/2009, you wrote:
>I already tried that approach, the records are archived at the Counties
>Office the representative from the Fire Marshals office dug thru the files
>for this facility unfortunately; everything prior to 1996 is gone.  The
>applicable codes at the time should have been 1991 UBC & UFC.  It's possible
>that this design was applicable at the time?  Again I find that hard to
>believe that Ord II was acceptable back then?
>
>Jim Johnston, P.E.
>Fire Protection Engineer
>Inland Fire Protection, Inc
>1100 Ahtanum Road
>Yakima, WA 98903
>Phone 509-248-4471
>Fax 509-248-1180
>[email protected]
>
>
>-----Original Message-----
>From: Scott A. Futrell [mailto:[email protected]]
>Sent: Thursday, December 17, 2009 3:06 PM
>To: [email protected]
>Subject: RE: Class III-A Combustible Liquids
>
>Your research needs to include the Building and Fire Code enforceable at
>the time of the original construction.  That will tell you what it
>should have been designed to, whether it was or wasn't won't be known
>until you start there.  Chris C. had a post about the LAW earlier today
>on another thread and that is the basis for the requirements you are
>trying to figure out.
>
>Scott Futrell
>
>(763) 425-1001 Office
>(612) 759-5556 Cell
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Jim
>Johnston
>Sent: Thursday, December 17, 2009 4:53 PM
>To: [email protected]
>Subject: RE: Class III-A Combustible Liquids
>
>It was existing at the time, so the hazard was present when originally
>installed.
>
>Jim Johnston, P.E.
>Fire Protection Engineer
>Inland Fire Protection, Inc
>1100 Ahtanum Road
>Yakima, WA 98903
>Phone 509-248-4471
>Fax 509-248-1180
>[email protected]
>
>
>-----Original Message-----
>From: Todd Williams [mailto:[email protected]]
>Sent: Thursday, December 17, 2009 2:44 PM
>To: [email protected]
>Subject: RE: Class III-A Combustible Liquids
>
>Was the building originally designed for the drum storage? Almost
>sounds like it was supposed to house something else.
>
>
>At 05:21 PM 12/17/2009, you wrote:
> >Unfortunately the person who designed this did it as Ord II and the AHJ
> >bought off on it.  I am pretty certain the codes never allowed this
>hazard
> >as Ord II, I just wanted to have some backing since I don't anything
>(NFPA
> >30) prior to 1993.  Nothing like trying to solve someone else's
>mistake.
> >
> >Jim Johnston, P.E.
> >Fire Protection Engineer
> >Inland Fire Protection, Inc
> >1100 Ahtanum Road
> >Yakima, WA 98903
> >Phone 509-248-4471
> >Fax 509-248-1180
> >[email protected]
> >
> >
> >-----Original Message-----
> >From: [email protected] [mailto:[email protected]]
> >Sent: Thursday, December 17, 2009 12:25 PM
> >To: [email protected]
> >Subject: RE: Class III-A Combustible Liquids
> >
> >OH II, no, don't think so.  Plus you may have issues with
>extinguishment
> >based on water alone since it's SG=.91 and is insoluble.
> >
> >
> >
> >
> >Craig L. Prahl, CET
> >Fire Protection Specialist
> >Mechanical Department
> >CH2MHILL
> >Lockwood Greene
> >1500 International Drive
> >PO Box 491, Spartanburg, SC  29304-0491
> >Direct - 864.599.4102
> >Fax - 864.599.8439
> >[email protected]
> >http://www.ch2m.com
> >
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of Jim
>Johnston
> >Sent: Thursday, December 17, 2009 3:07 PM
> >To: [email protected]
> >Subject: RE: Class III-A Combustible Liquids
> >
> >Craig,
> >  The liquid is spearmint oil flash point 143 F, the oil is stored in
> >non-relieving steel drums.  I have looked at the MSDS sheets and 2008
>NFPA
> >30 as well as a small section of NFPA 30 - 1993.  I am pretty
>comfortable
> >with requirements of 1993 and 2008 just don't have the backing of what
>the
> >requirements prior to 1993 were?  I just don't see it as Ordinary II?
> >
> >Jim Johnston, P.E.
> >Fire Protection Engineer
> >Inland Fire Protection, Inc
> >1100 Ahtanum Road
> >Yakima, WA 98903
> >Phone 509-248-4471
> >Fax 509-248-1180
> >[email protected]
> >
> >
> >-----Original Message-----
> >From: [email protected] [mailto:[email protected]]
> >Sent: Thursday, December 17, 2009 11:20 AM
> >To: [email protected]
> >Subject: RE: Class III-A Combustible Liquids
> >
> >I've found a lot of chemical protection systems designed per NFPA 13
>with
>no
> >regard to any other Standard.  Using the text in Chapter 5 within the
> >various Hazards they base their design solely on the description of
> >conditions and words such as "moderate" or "substantial".
> >
> >Protection of chemicals is in almost all cases beyond the scope of NFPA
>13
> >alone.  You need MSDS information as we've stated here on many
>occasions
>but
> >if you're not comfortable in analyzing chemical properties,
>compatibilities,
> >extinguishing methodology (other than water), then defer to someone
>with
>the
> >expertise.
> >
> >What can be especially tricky is when various types of chemicals are
>stored
> >in the same area.
> >
> >
> >The questions I'd be asking are how much of this chemical is present,
>(there
> >are code limitations), in what kind of area does this storage exist,
> >(dedicated chemical storage room/control area or out in the open plant
> >area), naturally ask for MSDS, you need to know whether it's a polar
>solvent
> >or hydrocarbon based material, miscibility, etc., etc., etc.  In some
>cases
> >a dry system may not be acceptable and you may have to go to non or
>single
> >interlocked preaction instead.  Lots of variables and lots of codes
>issues
> >to look at in these cases.
> >
> >
> >
> >
> >****And by the way I don't qualify as one of the old geezers, but I
>have
> >stayed in a Holiday Inn Express on more than one occasion.
> >
> >
> >
> >Craig L. Prahl, CET
> >Fire Protection Specialist
> >Mechanical Department
> >CH2MHILL
> >Lockwood Greene
> >1500 International Drive
> >PO Box 491, Spartanburg, SC  29304-0491
> >Direct - 864.599.4102
> >Fax - 864.599.8439
> >[email protected]
> >http://www.ch2m.com
> >
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of Jim
>Johnston
> >Sent: Thursday, December 17, 2009 12:42 PM
> >To: [email protected]
> >Subject: Class III-A Combustible Liquids
> >
> >Got a design criteria trivial question for some of the more experienced
>(PC
> >for the old geezers, lol).  A system installed in 1992 protecting Class
> >III-A Combustible liquids in 55 gallon non-relieving drums stored 3
>high
>was
> >designed as a dry system and to Ordinary II (.20 / 1950).  By today's
> >standards NFPA 30 is the applicable code, I assume it was back then
>too?
> >2008 NFPA 30 is drastically different than when the system was designed
>back
> >then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000
>(high
> >temp) or 5000 (ordinary temp) this is for water w/o foam.  My
>assumption is
> >the system was designed inadequate back in 1992 just don't have the
> >information to justify my statement.  Can any of my fellow comrades
>help me
> >out?
> >
> >
> >
> >Thanks in advance.
> >
> >
> >
> >Also I hope all of you a very Merry Christmas.
> >
> >
> >
> >Jim Johnston, P.E.
> >
> >Fire Protection Engineer
> >
> >Inland Fire Protection, Inc
> >
> >1100 Ahtanum Road
> >
> >Yakima, WA 98903
> >
> >Phone 509-248-4471
> >
> >Fax 509-248-1180
> >
> >[email protected]
> >
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email
>to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email
>to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email
>to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email
>to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email
>to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to